Service Mast Support
#1
Member
Thread Starter
Join Date: Oct 2013
Posts: 487
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Service Mast Support
The utility hooked up a new service drop cable. Is the way it is secured to the mast proper?
If you notice there are only 2 strands of that neutral wire connected to the clamp on the riser.
If you notice there are only 2 strands of that neutral wire connected to the clamp on the riser.
#5
Member
Thread Starter
Join Date: Oct 2013
Posts: 487
Upvotes: 0
Received 0 Upvotes
on
0 Posts
So the two strands on the clamp are probably steel? I didn't think of that... so the aluminum bear no brunt of the weight (and if it did it would snap no?)
And yes I realize if it falls they fix it.... but it also would fry the electronics in my home if the neutral is lost.
And yes I realize if it falls they fix it.... but it also would fry the electronics in my home if the neutral is lost.
#7
Member
Thread Starter
Join Date: Oct 2013
Posts: 487
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for clarifying for me.
The neutral wire itself, where it splits off to the clamp or the crimp... see where the strands are stretched/ spaced out a bit?
Is that ok?
The neutral wire itself, where it splits off to the clamp or the crimp... see where the strands are stretched/ spaced out a bit?
Is that ok?
Last edited by zmike; 08-10-15 at 07:12 AM.
#8
They didn't use any strands from the neutral to go thru the hook. The PoCo uses a plated all steel hanger. That part you see in the hook actually wraps around the service neutral.
Your service looks fine.... stop worrying.
Your service looks fine.... stop worrying.
#9
I don't know what this type attachment to the mast wire holder is called, but I have seen it used successfully in several areas. The utilities I am familiar with all use wedge clamps to attached the neutral of the ACSR service drop to the wire holder.
#10
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
The picture doesn't show how high the attachment point is above the roof but in my area a mast like that is required to have TWO backstays between 30 and 60 degrees off center from the cable to resist the pull of the service drop. Other power companies in my area would want at the very least a single backstay in line with the drop.