Air Conditioner service disconnect / fuses

I am installing a Quick Disconnect for a Mini-Split A/C condenser. The condenser (240V) requires a neutral conductor.

My question is do the neutral and ground conductors have to be electrically separate as the do in a sub panel?

Further, does the disconnect have to be fused or is the breaker in the main panel adequate for overcurrent protection?

Thanks,
-dmd-
 
Sponsored Links
  #2  
Old 08-11-15, 07:08 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 43 Votes on 41 Posts
The ground and neutral must be electrically separate. The neutral should not be disconnected by the pull-out disconnect switch, only the two hot conductors. The disconnect should be fused if the A/C manufacturer specifically requires it. Otherwise it can be an unfused disconnect with a proper breaker size according to the Max OCPD and Min Ckt Ampacity ratings from the A/C manufacturer.
 
  #3  
Old 08-11-15, 03:23 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,638
Received 83 Votes on 73 Posts
Further, does the disconnect have to be fused or is the breaker in the main panel adequate for overcurrent protection?
What is the MOCP from the data plate? 25 amp 2 pole breakers used to be quite rare and available by special order only, but since A-C units have gotten more efficient, 25 amp breakers are readily available at most supply houses and even at many box stores. If the MOCP is 35 amps, I would feed a 60 amp disconnect with a 40 amp or higher circuit and install 35 amp fuses. Some units will have a maximum fuse size on the data plate. I have seen a few inspectors who interpret that to mean that protection must be provided with fuses.

For the most part I like a 60 amp non-fused disconnect that can be purchased for under $6.
 
  #4  
Old 08-11-15, 07:09 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,144
Received 83 Votes on 71 Posts
If the nameplate states maximum fuse size, fuses must be used. If it just states maximum overcurrent fuses or breakers can be used.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: