Mini Split AC electrical
Hello, I have a 110v 1ton unit that needs 10 gauge power and 14 gauge control wire. Can they be in the same conduit and if so how large of a conduit is needed without any derating? Can the control just be 4x14 thwn instead of a special minisplit cable?
The indoor unit is powered from the outdoor unit over the 14/4
Thanks
The indoor unit is powered from the outdoor unit over the 14/4
Thanks
#2
The manufacturer's installation manual should specify which wiring is field provided and which is part of their unit or an assembly you must get from them. I have seen a variety of specifications for the wiring between the inside and outside unit -- depends on which ones you have. The mfr should provide minimum circuit ampacity (MCA) and maximum overcurrent protection device (Max OCPD) for the supply circuit. The supply circuit and control wires cannot be in the same conduit.
#3
Member
Thread Starter
Join Date: Oct 2014
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
15 MCA, 25 OCPD
It's not 240, straight 120.
It says 14/4 back to the indoor
Blue/Black/Brown/Ground on the interconnect
White/Black or Red/Ground to the outdoor
Can't put the interconnect in the same conduit
Gree 12,000 16seer unit
It's not 240, straight 120.
It says 14/4 back to the indoor
Blue/Black/Brown/Ground on the interconnect
White/Black or Red/Ground to the outdoor
Can't put the interconnect in the same conduit
Gree 12,000 16seer unit
#4
Blue/Black/Brown/Ground on the interconnect
With split units.... power goes to a service disconnect at the unit then to the condensor.
I use 14-3 UF cable and the cable follows along with the refrigerant and drain lines. The control cable comes in the back of the inside unit..... in the same opening as the refrigerant and drain lines.
The colors between the two units is of no consequence..... however you will see the numbers 1,2,3, and G. You must connect the same color to the same number at both ends.
Based on the Cree install manual and using 14-3 w/gr. UF cable between units.

And a word to the wise...... be sure you are familiar with the manufacturers warranty and the warranty policy from the place of purchase. Many times warranty and warranty repair is based on installation by an authorized installation company.
Last edited by PJmax; 08-12-15 at 08:23 PM. Reason: added wiring coloring info
#5
Member
Thread Starter
Join Date: Oct 2014
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I know NM is a no no outdoors, but can I run it to the disconnect and then switch to thwn? Technically there would be 6in of NM in an outdoor enclosure?
I'm not too concerned about warranty, unit and some of the install cost will be free after rebate
I'm not too concerned about warranty, unit and some of the install cost will be free after rebate
#7
The NM can go into the back of the disconnect. I usually cut a 2-3" piece of conduit screwed into the back of the disconnect, hole saw a 1" hole into the house and sleeve the NM through that. Fill in all the gaps with great stuff or caulk. You could use UF if you wanted.
No need for the supply circuit to be #10. According to the MCA this can be #14, #12 if it's a particularly long distance roughly 100' or more from the panel. I'd install a 20A breaker.
No need for the supply circuit to be #10. According to the MCA this can be #14, #12 if it's a particularly long distance roughly 100' or more from the panel. I'd install a 20A breaker.
#8
Member
Thread Starter
Join Date: Oct 2014
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
This is the breaker I want isn't it? For a Square D QO panels
Square D, QO 25 Amp Single-Pole Circuit Breaker, QO125CP at The Home Depot - Mobile
Seems odd none of my local half dozen store HD/Lowes have it in stock but the one HD/Lowes in a different smaller area does
Square D, QO 25 Amp Single-Pole Circuit Breaker, QO125CP at The Home Depot - Mobile
Seems odd none of my local half dozen store HD/Lowes have it in stock but the one HD/Lowes in a different smaller area does
#9
Member
Thread Starter
Join Date: Oct 2014
Posts: 18
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The manual says 10awg? 25amp breaker
http://www.homedepot.com/catalog/pdf...fa4d0ffb33.pdf
The 12k 115v model
http://www.homedepot.com/catalog/pdf...fa4d0ffb33.pdf
The 12k 115v model
#10
Indeed it does -- lots of contradictory instructions in that manual. Maybe contact them for clarification, or just use the #10. It won't hurt anything other than your wallet.
Usually with the max OCPD you should start with the smallest breaker to satisfy the MCA (15A in this case), and increase until you get to the Max OCPD if the unit will not start up without tripping the breaker. You can jump right to 25A, but it's generally best practice to try the smaller ones first.
This one is also a gem of confusion: Interconnecting Cable: Recommended cable - 14/4 AWG stranded bare copper conductors THHN 600V unshielded wire
Usually with the max OCPD you should start with the smallest breaker to satisfy the MCA (15A in this case), and increase until you get to the Max OCPD if the unit will not start up without tripping the breaker. You can jump right to 25A, but it's generally best practice to try the smaller ones first.
This one is also a gem of confusion: Interconnecting Cable: Recommended cable - 14/4 AWG stranded bare copper conductors THHN 600V unshielded wire
#12
You do not need to run the UF in anything. The UF follows and gets taped or tied directly to the refrigerant lines. The control cable doesn't need to follow the main power cable.
Most installations look like below. The AC comes to a service disconnect and then to the unit in Sealtite. There will be a second knockout next to where the power enters the unit for the control cable. The yellow/orange lines are the refrigerant lines. The black is the UF. The gray is the drain line.

Since most of the time I wire the system installed by an A/C contractor..... the lines between the two units are covered in a plastic covering that looks like a gutter downspout pipe.
Most installations look like below. The AC comes to a service disconnect and then to the unit in Sealtite. There will be a second knockout next to where the power enters the unit for the control cable. The yellow/orange lines are the refrigerant lines. The black is the UF. The gray is the drain line.

Since most of the time I wire the system installed by an A/C contractor..... the lines between the two units are covered in a plastic covering that looks like a gutter downspout pipe.