I have a series of receptacles in the garage. I am replacing the lead receptacle with the tamper proof gfci. The circuit worked before but now as soon as I put a load on the new tamper proof gfci the gfci kicks off & I cannot reset it. I have tried using another new tamper proof gfci & same thing happens. Please send me your help, this is for my husband. Thanks
 
  #2  
Old 08-21-15, 01:09 PM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 18,870
Received 1,188 Upvotes on 1,146 Posts
Welcome to the forums.

Was the original receptacle GFCI as well?
 
  #3  
Old 08-21-15, 02:08 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Disconnect any conductors that are connected to the load side of the GFCI and see if it resets.
Geo
 
  #4  
Old 08-21-15, 02:39 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
You also need to check that the power in cable connects to the line terminals.
 
  #5  
Old 08-21-15, 03:18 PM
J
Member
Join Date: Jan 2011
Location: USA
Posts: 4,459
Received 125 Upvotes on 110 Posts
Metal box? 100% sure none of the screws or bare wiring is touching the box?
There's two sides to a GFI outlet.
Look right on the back of the outlet, should say line and load.
Line is the incoming power, load is any outlets down line.
What load are you trying to plug in?
 
  #6  
Old 08-21-15, 05:40 PM
B
Member
Thread Starter
Join Date: Aug 2015
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Original circuit in series of 3 receptacle outlets, no gfci.
Wire is armoured bx cable in metal boxes.
12 gauge wire, 20 amp circuit
All working up till husband pulled first receptacle out of series to be replaced by tamper proof gfci.
The line side Ground wire was short in length so husband pulled on the line ground & got about an inch more wire. He pigtailed the 3 grounds together to connect to new gfci receptacle & installed a new
tamper proof gfci. Just hooking into line side the new gfci worked & he got power to portable fan.
When he hooked up load side for other 2 receptacles in series with new tamper proof gfci the gfci tripped. Husband could not reset at all. When husband disconnects load side & disconnected gfci from line power & reconnected gfci to line power gfci would work again. Husband replaced original new gfci with another new gfci (all tamper proof), and same results. Husband pulled electrical plate off electric panel to make sure circuit is connected properly & it was or is and it never tripped circuit breaker. Only thing different between new gfci replacing old receptacle was husband pulling a little bit of ground wire from line side to get enough wire to make a pigtail on ground side. Testing of the gfci has been done with the receptacle pulled out of metal boxes. No shorts & 120 on hot line side coming in, this is the whole story what do you think? Appreciate your help on this he is stumped!
 
  #7  
Old 08-21-15, 05:46 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Just hooking into line side the new gfci worked & he got power to portable fan.
When he hooked up load side for other 2 receptacles in series with new tamper proof gfci the gfci tripped.
It is one of the other two receptacles. At the second receptacle disconnect the cable to the third receptacle. Does the GFCI trip?
 
  #8  
Old 08-21-15, 06:23 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
Sounds like there is an issue downstream of the gfi. Since you only have two receptacles to check it should not be hard to locate the issue. Make sure nothing is plugged in when testing.
 
 