Connecting exhaust fan above shower

Reply

  #1  
Old 08-22-15, 05:03 PM
Member
Thread Starter
Join Date: Aug 2013
Location: USA
Posts: 72
Connecting exhaust fan above shower

Hello,

I'm installing an exhaust fan above a shower in a new bathroom I'm building. There's a note in the manual that if installed above a shower it must tie into a GFCI protected branch circuit. I'm planning on having a dedicated circuit for the GFCI outlet next to the sink. Can I tie the exhaust fan (and only the exhaust fan) into this circuit via the GFCI's LOAD screws? I can't remember whether not not the GFCI outlet net to the sink has to be by itself. If it matters the type of fan and watt rating is below.

UPDATE: I'm also installing lights above the shower and apparently they have the same GFCI requirement. So perhaps I'll just do the GFCI at the breaker for the two lights and the fan. Is this doable?

Thanks!



 
Sponsored Links
  #2  
Old 08-22-15, 05:13 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,221
I'm planning on having a dedicated circuit for the GFCI outlet next to the sink. Can I tie the exhaust fan (and only the exhaust fan) into this circuit via the GFCI's LOAD screws?
As long as the new 20 amp circuit serves only this one bathroom, yes, you can power the fan from the load side of the GFCI receptacle. The easier and more common way would be to not put the fan over the footprint of the shower.
 
  #3  
Old 08-22-15, 05:22 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,362
I have never seen lights that required gfi protection over a shower or tub.
 
  #4  
Old 08-22-15, 05:39 PM
Member
Thread Starter
Join Date: Aug 2013
Location: USA
Posts: 72
pcboss: I have never seen lights that required gfi protection over a shower or tub.
You're correct, I wen't back and double checked the box and noticed I misread the NEC comment.

CasualJoe: The easier and more common way would be to not put the fan over the footprint of the shower.
It's not an option, hard to explain why but it's simply not an option to move it out of the shower. It's a large shower with a high ceiling so its' ok with me.

Other thoughts, I'm going to need two circuits in the bathroom regardless so I'll just plan on making the fan and lights on the same GFCI breaker\circuit.

Thanks for the help!
 
  #5  
Old 08-23-15, 08:13 AM
Member
Join Date: Mar 2010
Location: USA
Posts: 2,860
It is aerodynamically advantageous to put the exhaust fan above a shower (or near the toilet at about tank level).

It does not hurt to put the exhaust fan on a ground fault circuit interrupter protected line.
 
  #6  
Old 08-23-15, 09:57 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,221
It does not hurt to put the exhaust fan on a ground fault circuit interrupter protected line.
In the OP's case, a GFCI protected circuit is a requirement.
 