Main panel replacement plans
#1
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Main panel replacement plans
I'm replacing my old 200-amp Federal Pacific panel (from 1975) with a Square-D Homeline (unless somebody convinces me that QO is worth it).
Here's the Federal Pacific panel I'm replacing:

Some comments on the picture:
- There's no main breaker!
- A 70-amp breaker goes to an external Federal Pacific subpanel for my two A/C units.
- 30-amp breaker is for clothes dryer
- 50-amp breaker is for oven
- 70-amp breaker in the middle of the box is wired to isolated bus bars in the bottom half of the panel, and that's where my 11 branch circuits are located
- I have an existing grounding wire bonded to the plumbing at the hot water heater, but no external grounding rods.
Some concerns with the existing wiring:
1. Although my house wiring is copper, it looks like the wires from the meter are aluminum. Do you agree? If so, do I need to replace these? (That seems not safe for me to do since I'd have to work in the meter box.)

2. It looks like the wire to my oven has experienced some oxidation. Can I just cut the green end off and strip the wire again? If not, what's the solution? Re-running this wire is not feasible.

My plan:
1. Submit permit application.
2. Remove drywall and prep area as much as possible before disconnecting power.
3. Install 8' grounding rod outside and run copper wire through wall below existing panel.
4. Schedule power company to pull meter. Schedule inspector.
5. Run extension cord to neighbor's house for lights/fridge.
6. Power company removes power.
7. Label all circuits.
8. Disconnect all circuits and remove old panel.
9. Install new panel.
10. Install all circuits on the same sides as they are now with the same breaker sizes that I have now.
11. Pass inspection.
12. Power company restores power.
Am I missing anything big?
Additional questions:
1. The Homeline panel is aluminum. Will I need anti-oxidizing compound anywhere in the box if my wiring is copper?
2. Am I required to use AFCI breakers?
3. In the new panel, what size copper wire do I use to bond the neutral and ground bars?
4. When running the copper wire for my new grounding rod, will the copper wire just simply exit the house about 2 feet above the ground, run down the brick, and go into the ground? Or do I need to add conduit for this wire?
Thanks for your help!!!
Here's the Federal Pacific panel I'm replacing:

Some comments on the picture:
- There's no main breaker!
- A 70-amp breaker goes to an external Federal Pacific subpanel for my two A/C units.
- 30-amp breaker is for clothes dryer
- 50-amp breaker is for oven
- 70-amp breaker in the middle of the box is wired to isolated bus bars in the bottom half of the panel, and that's where my 11 branch circuits are located
- I have an existing grounding wire bonded to the plumbing at the hot water heater, but no external grounding rods.
Some concerns with the existing wiring:
1. Although my house wiring is copper, it looks like the wires from the meter are aluminum. Do you agree? If so, do I need to replace these? (That seems not safe for me to do since I'd have to work in the meter box.)

2. It looks like the wire to my oven has experienced some oxidation. Can I just cut the green end off and strip the wire again? If not, what's the solution? Re-running this wire is not feasible.

My plan:
1. Submit permit application.
2. Remove drywall and prep area as much as possible before disconnecting power.
3. Install 8' grounding rod outside and run copper wire through wall below existing panel.
4. Schedule power company to pull meter. Schedule inspector.
5. Run extension cord to neighbor's house for lights/fridge.
6. Power company removes power.
7. Label all circuits.
8. Disconnect all circuits and remove old panel.
9. Install new panel.
10. Install all circuits on the same sides as they are now with the same breaker sizes that I have now.
11. Pass inspection.
12. Power company restores power.
Am I missing anything big?
Additional questions:
1. The Homeline panel is aluminum. Will I need anti-oxidizing compound anywhere in the box if my wiring is copper?
2. Am I required to use AFCI breakers?
3. In the new panel, what size copper wire do I use to bond the neutral and ground bars?
4. When running the copper wire for my new grounding rod, will the copper wire just simply exit the house about 2 feet above the ground, run down the brick, and go into the ground? Or do I need to add conduit for this wire?
Thanks for your help!!!
#2
Lots of questions.... make several replies to get to them all.
That is a Federal split bus panel. You technically have three main breakers there. One for the lower section, one for the oven and one for the clothes dryer. I was never a big fan of that type of panel. That's one good reason to change.
The Federal breaker problems is another good reason to upgrade.
I don't really know what the difference between Homeline and QO is but as an electrician I always use QO. The price difference is not substantial.
The wires that are oxidized can be cut back and re-stripped.
Aluminum service wiring.... from the panel to the meter is very common. That cable should have NoOx on it at the main breaker.
1. The Homeline panel is aluminum. Will I need anti-oxidizing compound anywhere in the box if my wiring is copper?
No.
2. Am I required to use AFCI breakers?
You are not required to upgrade to AFCI during a panel replacement.
3. In the new panel, what size copper wire do I use to bond the neutral and ground bars?
The new panel comes with a long green screw that bonds the neutral to ground. You can get an additional bar for just the grounds which would be bonded by the mounting screws.
4. When running the copper wire for my new grounding rod, will the copper wire just simply
exit the house about 2 feet above the ground, run down the brick, and go into the ground? Or do I need to add conduit for this wire?
Protection is not required. Clamps to hold the #6 wire neatly to the wall is a good idea.
This may not be a one day process. The inspectors give a broad range of inspection times and sometimes come late in the day. The power company needs a cut-in card (proof of passing inspection) and they will be in no rush to reconnect you. So that this may be a two day process.
That is a Federal split bus panel. You technically have three main breakers there. One for the lower section, one for the oven and one for the clothes dryer. I was never a big fan of that type of panel. That's one good reason to change.
The Federal breaker problems is another good reason to upgrade.
I don't really know what the difference between Homeline and QO is but as an electrician I always use QO. The price difference is not substantial.
The wires that are oxidized can be cut back and re-stripped.
Aluminum service wiring.... from the panel to the meter is very common. That cable should have NoOx on it at the main breaker.
1. The Homeline panel is aluminum. Will I need anti-oxidizing compound anywhere in the box if my wiring is copper?
No.
2. Am I required to use AFCI breakers?
You are not required to upgrade to AFCI during a panel replacement.
3. In the new panel, what size copper wire do I use to bond the neutral and ground bars?
The new panel comes with a long green screw that bonds the neutral to ground. You can get an additional bar for just the grounds which would be bonded by the mounting screws.
4. When running the copper wire for my new grounding rod, will the copper wire just simply
exit the house about 2 feet above the ground, run down the brick, and go into the ground? Or do I need to add conduit for this wire?
Protection is not required. Clamps to hold the #6 wire neatly to the wall is a good idea.
This may not be a one day process. The inspectors give a broad range of inspection times and sometimes come late in the day. The power company needs a cut-in card (proof of passing inspection) and they will be in no rush to reconnect you. So that this may be a two day process.
#3
You should label the circuits before loosing power.
Once the meter is pulled the power is gone.
Plan on two ground rods at least 6' apart.
The copper oven wire looks like it got wet. A light wire brushing should remove corrosion.
Aluminum conductors are safely used to feed panels everyday.
Once the meter is pulled the power is gone.
Plan on two ground rods at least 6' apart.
The copper oven wire looks like it got wet. A light wire brushing should remove corrosion.
Aluminum conductors are safely used to feed panels everyday.
#4
Best to rent a generator before you do it or consider hiring an electrician. Unlike the home owners electricians can get a way with doing a temporary connection and could probably finish in a day.
#5
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Wow, thank you so much for the excellent responses!
I will re-consider a QO panel. I priced it out (with breakers) at $270 vs $170 for Homeline. The breakers cost 2x. Biggest difference I see is that QO is copper and Homeline is aluminum.
I will install 2 grounding rods, spaced 6-feet apart connected to a single #6 copper wire.
Good point in planning for a 2-day install. I'll be sure to do it mid-week rather than a Friday just in case.
Thanks again!
Additional questions:
1. Instructions I've seen say to install breakers starting at the top of the panel and work down. Is that a requirement, or is it just to look pretty? I might like to leave room at the top for a whole-house surge protector or a new 240V car charging outlet.
I will re-consider a QO panel. I priced it out (with breakers) at $270 vs $170 for Homeline. The breakers cost 2x. Biggest difference I see is that QO is copper and Homeline is aluminum.
I will install 2 grounding rods, spaced 6-feet apart connected to a single #6 copper wire.
Good point in planning for a 2-day install. I'll be sure to do it mid-week rather than a Friday just in case.
Thanks again!
Additional questions:
1. Instructions I've seen say to install breakers starting at the top of the panel and work down. Is that a requirement, or is it just to look pretty? I might like to leave room at the top for a whole-house surge protector or a new 240V car charging outlet.
#6
You can put the breakers wherever, top or bottom. . You can even leave spaces open for future use.
#7
QO also gives you the Visi-trip indicators which are orange flags to show a tripped breaker quickly.
#8
Like PCboss said you can put the breakers wherever you want but the length of the existing wires will dictate the placement also. You don't want to have to extend a lot of wires in the panel if it can be helped.
#10
Banned. Rule And/Or Policy Violation
Join Date: Jul 2009
Location: usa
Posts: 87
Upvotes: 0
Received 0 Upvotes
on
0 Posts
> 4. When running the copper wire for my new grounding rod, will the copper wire just
> simply exit the house about 2 feet above the ground, run down the brick, and go
> into the ground? Or do I need to add conduit for this wire?
Code defines that ground is necessary for human safety. And defines what is minimal (ie why two copper clad ground rods). But ground also serves a second function. It is the only device that does protection for household appliances. Length of that connection and how it is routed determines whether a 'whole house' solution will be effective or ineffective.
For example, if that ground wire is inside metallic conduit, then protection is completely compromised; earth ground is all but disconnected. That wire must route to ground electrodes as directly (straight) as possible, away from other non-grounding wires, no sharp bends, and no splices. it must be the single point earth ground - all four words have electrical significance.
Ground electrodes must also be installed so that all other incoming utility wires (ie cable, telephone, dish, roof antenna) also make a low impedance (ie less than 10 foot) connection to those same electrodes. All this exceeds code requirements for human safety. And is essential for transistor safety.
An AC utility demonstrates good, bad, and ugly (preferred, wrong, and right) solutions:
Tech Tip 08 -Duke Energy
> simply exit the house about 2 feet above the ground, run down the brick, and go
> into the ground? Or do I need to add conduit for this wire?
Code defines that ground is necessary for human safety. And defines what is minimal (ie why two copper clad ground rods). But ground also serves a second function. It is the only device that does protection for household appliances. Length of that connection and how it is routed determines whether a 'whole house' solution will be effective or ineffective.
For example, if that ground wire is inside metallic conduit, then protection is completely compromised; earth ground is all but disconnected. That wire must route to ground electrodes as directly (straight) as possible, away from other non-grounding wires, no sharp bends, and no splices. it must be the single point earth ground - all four words have electrical significance.
Ground electrodes must also be installed so that all other incoming utility wires (ie cable, telephone, dish, roof antenna) also make a low impedance (ie less than 10 foot) connection to those same electrodes. All this exceeds code requirements for human safety. And is essential for transistor safety.
An AC utility demonstrates good, bad, and ugly (preferred, wrong, and right) solutions:
Tech Tip 08 -Duke Energy
#11
I will re-consider a QO panel. I priced it out (with breakers) at $270 vs $170 for Homeline. The breakers cost 2x. Biggest difference I see is that QO is copper and Homeline is aluminum.
Considering the age of your existing service (at least 30 years old now), I believe I'd replace the meter socket and all service entrance wiring too.
#12
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'll have a look at the CH series. The $100 price difference between Homeline and QO doesn't bother me at all as long as it's worth it. From comments here, it sounds like it's worth it.
I'm not sure how I'd replace the meter socket since the utility-side in the socket will still be hot. Is there a specific concern with old sockets and service wiring?
I'm not sure how I'd replace the meter socket since the utility-side in the socket will still be hot. Is there a specific concern with old sockets and service wiring?
#13
Is there a specific concern with old sockets and service wiring?
How does the meter pan look..... clean... not rusted ?
I see conduit coming in to feed the panel.
Is the service going up the house also in conduit.... or is it an underground service ?
You may have to get into the meter pan if the wiring currently coming in from outside isn't long enough.
#14
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
From the outside, the meter pan looks ok to me. All wires are in conduit. The conduit from the panel to the meter is entirely within the exterior wall. The meter is fed from underground service.
How would I safely work inside the meter pan?
How would I safely work inside the meter pan?
#16
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok, I'll ask the power company about disconnecting the power at the transformer.
Now I'm concerned that my service entrance cable might be too short when I try to connect it to my new panel. Am I right to assume that the power would still have to be disconnected at the transformer to replace only the service entrance cable? Or is there a safe way to work in the meter socket with hot wires? (My guess is no.)
Now I'm concerned that my service entrance cable might be too short when I try to connect it to my new panel. Am I right to assume that the power would still have to be disconnected at the transformer to replace only the service entrance cable? Or is there a safe way to work in the meter socket with hot wires? (My guess is no.)
#17
Not for someone without live work training, tools and PPE. It's not something you want to try. Youtube arc flash videos for several good reasons why.
The power company shouldn't really have a problem disconnecting at the transformer, although you might want to let them know in advance so they can send the correct technician on the call. The guys who work meters aren't always the same ones who work transformers.
The power company shouldn't really have a problem disconnecting at the transformer, although you might want to let them know in advance so they can send the correct technician on the call. The guys who work meters aren't always the same ones who work transformers.
#18
Now I'm concerned that my service entrance cable might be too short when I try to connect it to my new panel.
#19
You can also do a complete new service including mast and meter socket next to the existing panel and service. When the new one is complete then you call the electric company to move the drop. After moving the existing panel can be gutted and used as a junction box to extend existing circuits to the new panel.
This has a couple of advantages. Your not without power while doing the new service so you can relax and take your time. Add a couple of receptacles to the new panel when you set it up and you will have power for essentials after the drop has been moved and your moving the circuits to the new panel.
This has a couple of advantages. Your not without power while doing the new service so you can relax and take your time. Add a couple of receptacles to the new panel when you set it up and you will have power for essentials after the drop has been moved and your moving the circuits to the new panel.
#20
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
A friend sent me a picture of the new Homeline panel his electrician installed 2 years ago. The conductors from the meter enter the panel in a location where I've never seen factory knockouts in any Square-D picture. Am I allowed to drill my own hole in the cabinet to avoid having to install longer conductors from the meter?

#21
You can drill knockout, but need to be aware of minimum bend radius requirements. You will not be able to use the back for a 200 amp service.
#22
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok, so are you saying that my friend's panel actually violates code since it's 200 amps?
Do you know where in the code the bend radius requirement is for these service conductors?
Do you know where in the code the bend radius requirement is for these service conductors?
#23
Maybe -- It's article 312.6 The minimum box depth from the end of the fitting to the box edge (cover in this case), in the direction of wire travel, for #4/0 wires is 4" and for #2/0 wires is 3.5". If the installer used #2/0 copper it may be compliant with NEC. If they used #4/0 aluminum it is probably not compliant with NEC, but the inspector may have approved it anyway.
It is also bad practice to wire tie all the conductors like that due to significant heat build up in the center of the bundle. Wires can be loosely grouped in the panel, but should not be tightly bound like structured data cables can be. Depending on how long those conduits are at the top of the panel, and how the cables are fastened on the other side, there could be a significant bundling problem there too.
It is also bad practice to wire tie all the conductors like that due to significant heat build up in the center of the bundle. Wires can be loosely grouped in the panel, but should not be tightly bound like structured data cables can be. Depending on how long those conduits are at the top of the panel, and how the cables are fastened on the other side, there could be a significant bundling problem there too.
#24
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Great information! I see the table in NEC that you're talking about. But if the conductor enters at the back of the panel, wouldn't table 312.6(B) be the one to use? In that case a #4/0 copper conductor would require 7"! Am I reading that right?
#27
All the cables in the two connectors in the center and both sides of the panel are violation too.
Last edited by pcboss; 08-31-15 at 07:16 PM.
#28
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Looking more closely at tables 312.6(A) and 312.6(B), aren't these requirements just saying how far away from the wall of the enclosure the lugs have to be based on wire size? Isn't this a requirement for the panel manufacturer more than the installer?
#29
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Snapped some pics of my meter. To my untrained eye, it seems ok. (Looks like there's an old tag sitting on top.) Anybody see something I should be concerned about?
Tried to get the power company to tell me how much they would charge to pull my meter, and they wouldn't tell me. They said it depends on labor and materials and said $200 wouldn't be surprising. Seems really high to me. I've seem them pull my meter half a dozen times in the last year because of wire issues on their side. It took 30 seconds each time! Anybody here in the Oncor service area in Texas have any experience with this?



Tried to get the power company to tell me how much they would charge to pull my meter, and they wouldn't tell me. They said it depends on labor and materials and said $200 wouldn't be surprising. Seems really high to me. I've seem them pull my meter half a dozen times in the last year because of wire issues on their side. It took 30 seconds each time! Anybody here in the Oncor service area in Texas have any experience with this?




#30
There should only be a minimal charge to pull the meter. If they had to disconnect at the transformer pad so that you could change the meter pan..... that runs around $275.00 here.
#33
Your friends panel is also missing a bushing on the connector for the service conductors.
#35
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Decided to ask my inspector directly about drilling a hole in the panel for my service entrance conductors. The response I got back wasn't yes or no. I need help from those who have worked with inspectors before. This inspector has been incredibly responsive and helpful so far. I don't get the impression at all that he's out to get me.
Here was his response when I asked about drilling my own hole:
When I asked for clarification, his response:
Now, the installation instructions don't say anything about drilling my own holes (allowed or not), and I think this is the inspector's way of saying "use common sense." Seems to me as long as I don't drill through a bus bar or something crazy like that, and as long as I comply with NEC 338.24 for service entrance bend radius requirements, I should be ok. Anybody disagree?
Here was his response when I asked about drilling my own hole:
The manufacturer of the panel makes them with specific areas for connections into the panel. Altering entry areas may interfere with the electrical components such as the bus bars, dedicated breaker spaces or grounding. Entering from other than what the manufacturer provides may also hinder proper bending radius of the service entrance conductors.
I'm saying follow the manufacturer's installation instructions regarding entries into that panel.
#36
Comercial panel enclosures can be ordered without factory knockouts so entries need to be drilled. As long as you follow bend radius concerns I don't see an issue .
#37
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
My 200A entrance runs through 1.5" metallic conduit into the back of the panel. Will a 1.5" insulated grounded bushing comply with code? Or do I need something else?
#38
My 200A entrance runs through 1.5" metallic conduit into the back of the panel. Will a 1.5" insulated grounded bushing comply with code? Or do I need something else?
If the knockouts are concentric with rings remaining, you need a bonding bushing on each end of the metallic conduit. If there are no rings remaining or if the knockout is eccentric (punched the correct size), you would use a grounding locknut. It is possible in some installations to have a bonding bushing on one end and a grounding locknut on the other end.
#39
Member
Thread Starter
Join Date: Feb 2014
Location: USA
Posts: 132
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks CasualJoe. I need a bonding bushing if the knockouts are concentric because concentric knockouts are electrically compromised? And that's different than eccentric knockouts?
The existing 1.5" conduit definitely looks roomy for the 3 service conductors in my old panel. I'm trying to avoid swapping out either the conduit or the conductors to keep my hand out of the meter socket.
Most likely I'm going to drill my own 2" hole for the 1.5" conduit so it lines up exactly with the hole in my old panel. In that case, I would just need a grounding locknut and plastic bushing, right?
The existing 1.5" conduit definitely looks roomy for the 3 service conductors in my old panel. I'm trying to avoid swapping out either the conduit or the conductors to keep my hand out of the meter socket.
Most likely I'm going to drill my own 2" hole for the 1.5" conduit so it lines up exactly with the hole in my old panel. In that case, I would just need a grounding locknut and plastic bushing, right?
#40
I'm going to drill my own 2" hole for the 1.5" conduit so it lines up exactly with the hole in my old panel. In that case, I would just need a grounding locknut and plastic bushing, right?