Have a pole barn w/concrete floor. Its 400' behind our home and would like to put power in it for lights and outlets for small tools and an air compressor (220). what size direct bury cable or wire would I need for say 50 amp service at best maybe less
 
Sponsored Links
  #2  
Old 08-30-15, 10:55 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,050
If you use aluminum MFE (Mobile Home Feeder) you would be looking at 2/0-2/0-1-4.
 
  #3  
Old 08-30-15, 10:59 AM
Member
Thread Starter
Join Date: Aug 2015
Location: usa
Posts: 2
is that direct bury cable I believe the code here is 18" deep not a problem to bury its all pasture land
 
  #4  
Old 08-30-15, 02:02 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,968
It would be 24" if unprotected by conduit. Of course check to make sure.
 
  #5  
Old 08-30-15, 02:09 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,282
Direct burial is 24". In conduit (PVC) it is 18". You might want to consider also burying a low voltage cable for internet/phone service. Bury that at about 12".
 