What flex cable to use in wet environment?
#1
Member
Thread Starter
What flex cable to use in wet environment?
I need to run some cable from an outside timer to power another receptacle (the second is more like an extension).
What type of electric cable can I use for this?
Wet location flexible?
It's a wall in use cover connected to a timer, which I will context to another receptacle with in use cover for gutter cable.
Or some kind of pipe between them?
http://postimg.org/image/sib8ufisp/
What type of electric cable can I use for this?
Wet location flexible?
It's a wall in use cover connected to a timer, which I will context to another receptacle with in use cover for gutter cable.
Or some kind of pipe between them?
http://postimg.org/image/sib8ufisp/
#2
Your link is a pay-to-see link. Either UF-b buried 24" or conduit with individual conductors buried 18". If the amps are 20 or less and there is GFCI protection at the beginning of the feed either can be one foot.
#3
Member
Thread Starter
Hmm. If you click cancel then it should show further down page.
Does it have to be minimum 1 ft long?
I'm not burying this cable, it runs from a gfci wall outlet to a weatherproof timer and then I need to connect 2 gutter cables (plugs not weather proof but probably W rated).
Does it have to be minimum 1 ft long?
I'm not burying this cable, it runs from a gfci wall outlet to a weatherproof timer and then I need to connect 2 gutter cables (plugs not weather proof but probably W rated).
#4
Does it have to be minimum 1 ft long?
#5
Member
Thread Starter
Try this: View image: Screenshot 2015 09 11 16 56 18
It needs to be mounted on cladding on a back wall of a house... nothing buried. The grey cable in the picture should be what type of wire if outside?
[ATTACH]
It needs to be mounted on cladding on a back wall of a house... nothing buried. The grey cable in the picture should be what type of wire if outside?

Last edited by ray2047; 09-11-15 at 02:53 PM. Reason: Add image.
#6
The box in your picture is not suitable for use outside. You will need a weather proof box
and an in use cover. 
At the existing box surface mount a single gang waterproof PVC box over the existing box.

Connect the two boxes with PVC conduit and run THWN wire between them. It would be mounted between the two receptacle boxes.
Problem is that timer may not be suitable for outdoor use and i see no safe way to connect it. I'd suggest hard wiring a weatherproof timer instead or a box mountable programmable timer in a single gang box with in use cover.


At the existing box surface mount a single gang waterproof PVC box over the existing box.

Connect the two boxes with PVC conduit and run THWN wire between them. It would be mounted between the two receptacle boxes.
Problem is that timer may not be suitable for outdoor use and i see no safe way to connect it. I'd suggest hard wiring a weatherproof timer instead or a box mountable programmable timer in a single gang box with in use cover.
Last edited by ray2047; 09-11-15 at 03:09 PM.
#7
Member
Thread Starter
Thanks.
I'm not 100% clear.
The existing wall gfci receptacle is a single gang with in use cover. The timer says it is weather proof but then it hangs outside the in use cover.
How do I take a PVC conduit from the timer into the new gang box so I can plug multiple devices into the timer?
The timer only has space for one receptacle.
I'm not 100% clear.
The existing wall gfci receptacle is a single gang with in use cover. The timer says it is weather proof but then it hangs outside the in use cover.
How do I take a PVC conduit from the timer into the new gang box so I can plug multiple devices into the timer?
The timer only has space for one receptacle.
#8
I said I didn't think the timer could be used.
But the male fitting has no way to protect a plug that is in it from the weather.
You can't. That is the second reason why it can't be used and why I wrote:
The timer says it is weather proof
How do I take a PVC conduit from the timer into the new gang box so I can plug multiple devices into the timer?
I'd suggest hard wiring a weatherproof timer instead or a box mountable programmable timer in a single gang box with in use cover.
#9
Member
Thread Starter
This is the timer... it says rain proof...
I know what you're saying, a plug goes into it so how can it be fully rain proof. The receptacle on the timer seems to be quite deep/recessed
I know what you're saying, a plug goes into it so how can it be fully rain proof. The receptacle on the timer seems to be quite deep/recessed
#10
I am not comfortable using that timer in the manner you want to use it. It is probably okay if used with a single plug as intended but you want to increase its capacity to multiple plugs. That I don't see a really good way to do. Perhaps someone else can help you. My only suggestion would be to put every thing in a large water proof box. If you used a commercially available box for electrical work it might be rather expensive or you could build one but of course home built would not be a UL improved enclosure and might violate local code.
Last edited by ray2047; 09-12-15 at 07:51 AM.