Hello, I am new to this site. I am redoing my basement which is down to the studs ( makes it easier). At this time i am wiring the electrical and want to make sur i am on the right track. I did my previous houses basement with an electrician friend but he has move away, so trying to remember what i did last time.
attached is a pic of what i am doing,
Any help or push in right direction would be great
Thanks
 
Attached Images  
Sponsored Links
  #2  
Old 09-11-15, 02:00 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,506
Looks reasonable, with a couple comments. Receptacles in the unfinished / storage areas need to be GFCI protected. Is wiring in the bathroom pre-existing? If not, you'll need a 20A GFCI protected circuit for the bathroom receptacles, lights and fan. Also it is customary for bathroom doors to enter inward -- looks akward opening into the kitchenette. I assume the narrow column in the center is a stairwell? Code requires the lighting in the stairwell have 3-way switches at the top and bottom. If the door at the top is an exit to the outside, an exterior switched light is required there.
 
  #3  
Old 09-11-15, 02:08 PM
Member
Thread Starter
Join Date: Sep 2015
Location: USA
Posts: 2
Yes the bathroom wiring is preexisting. currently the door does open out but is being replaced with another door that opens in. thank you for your help. I will make a note of the gfci in the mechanical room and the storage area. Right now there is a 3way switch at the top of the stairs and another switch at the back door. need to move the one at the back door to the bottom of the stairs then. Thanks again.
 
  #4  
Old 09-11-15, 03:52 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
You don't need to move the switch , just add a 4 way to the existing.
 
  #5  
Old 09-11-15, 07:42 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,385
Code requires the lighting in the stairwell have 3-way switches at the top and bottom.
In my area those 3-way switches must be lighted devices, but that might be a local building code issue. I don't believe it is covered in the NEC.

Assuming you are wiring to the 2011 or 2014 NEC, remember that each switchbox must have a neutral conductor whether it is used or not.
 
  #6  
Old 09-12-15, 07:38 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,279
If it was me I would split the red circuit into two 15 amp circuits.

Only the bathroom receptacle(s) are required to be 20 amp. The lights and fan is not.

Also per code everything other then the bathroom and storage is required to be AFCI protected. All receptacles are required to be tamper resistant.
 