Need help changing a 220 outlet to a 120.
Old 09-18-15, 02:52 PM
Hey guys, I have a 220 outlet near a window in my house that was originally for a window AC unit..
I now want to change it to a normal 120 outlet receptacle. How would I go about doing this?
Here is my 220 outlet current set up:
I have a red, a white and a black. The white is taped off and not connected to anything.
This is my panel (very old, but still functioning just fine).
I believe that the very bottom fuse controls that 220 outlet because when I was removing the outlet, I'm assuming two wires touched and arched and then that fuse was popped.
Old 09-18-15, 03:03 PM
Note that this site bans links to tiny pic due to amount of spam images on that service.
To convert this you would need to cap off the red wire and connect the receptacle to the black, white and bare. You would need to verify the protecting fuse is no greater than 20A. Something that is concerning is your ground wire appears to be bare aluminum and the circuit conductors seem to be copper. If you actually have aluminum wire then you have a potentially significant problem on this circuit.
Old 09-18-15, 03:32 PM
Sorry I did not know about the Tiny pic rule.
Thanks for the help. I am assuming I would connect the bare wire to the ground screw on the outlet?
Also, the wire is bare aluminum from the way it looks. What does that mean problem wise? And how would I correct it?
All fuses in the panel are 20A.
Old 09-18-15, 04:38 PM
ray2047's Avatar
And pigtail it to the box. If it is aluminum that can't be done with a wire nut but I suspect it is tinned copper. Look at a a cross section of the cut wire. Do you see copper? If too hard to see cut at 45 to give more cut area to look at.
Old 09-18-15, 06:03 PM
pcboss's Avatar
I suspect that is the bond wire from the AC cable that someone did not know what to do with. It looks too small to be aNY thing else.
Old 09-18-15, 07:12 PM
CasualJoe's Avatar
If the 240 volt circuit is connected to screw in fuses, there would be one fuse for the black wire and one fuse for the red wire.