Grounding an outdoor metal weather resistant receptacle box

Iím installing an outdoor GFCI receptacle in a metal weather resistant box. The box has a ground screw. Does NEC require a ground wire be attached to the screw? I am running 3 wires from an outdoor load center (black, white, green) to the box to attach to the GFCI receptacle. Should I splice the ground wire from the load center in the receptacle box and attach one wire to the box and one wire to the receptacle? Or should I run a 2nd ground wire from the load center to the receptacle box and attach that to the ground screw. Both the load center and the reputable box are in very close proximity.

Thanks for your help!
 
  #2  
Old 09-21-15, 07:23 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
If the conduit is metallic it is optional. If it is non metallic cable or non metallic conduit pigtail ground to both the box and the receptacle.
 
  #3  
Old 09-21-15, 07:27 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,704
Received 662 Upvotes on 562 Posts
Yes, you need to connect the green wire to the metal box. Their are many ways to do it, easiest for a DIYer would be to connect a pigtail (green or bare) to the metal box and another pigtail to the device. Then splice the two pigtails to the green wire with a nut.
 
 