Difference between new construction breaker panel and a retrofit

Hi all

I'm shopping for a new breaker panel. My home currently has a 150 stab lok federal pioneer I need to change out to a 200 amp. So far I've just been looking online and I see some panels advertised as retrofit panels. They all look the same to me so I'm wondering if that is just a gimmick or they are somehow made differently to make install easier?

Also I know most guys swear by Square D but I'm leaning towards a 200 amp 40/80 cutler hammer panel linked below. It seems like a decent deal and comes with about half the breakers I'll need. Also I had a cutler hammer at my last house so I'm used to working on it. Any reason to avoid that panel?

Thanks!

Eaton Cutler-Hammer | 200A 40/80 Circuit Indoor Arc Fault Panel Package With 15A Arc Fault Breaker and Dnpl Breakers | Home Depot Canada
 
  #2  
Old 09-23-15, 06:40 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,471
Received 83 Upvotes on 75 Posts
True retrofit panels just include the guts and a cover. You can leave your current box in place and don't have to re-feed wires. It saves a lot of work if your old panel is flush in a wall cavity.
 
  #3  
Old 09-23-15, 08:36 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
One retrofit panel has terminals to splice any wires that are too short instead of wire nuts. One also has end panels that make it easy to connect the cables without needing to hold the entire panel.
 
  #4  
Old 09-23-15, 08:56 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Eaton BR series and Square D Q0 series are both quality brands with good history of long performance. Not sure if it's the same in Canada, but one significant difference between the two is Square D has lifetime warranty and Eaton BR has 10 year warranty. Note that Cutler is now an Eaton brand that is sold under the CH series. It is similar quality and price to Square D, also with a lifetime warranty. BR is Eaton's more budget friendly series, but still quite good.
 
  #5  
Old 09-23-15, 10:45 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,825
Received 366 Upvotes on 326 Posts
My home currently has a 150 stab lok federal pioneer I need to change out to a 200 amp...
If you're upgrading the main breaker, you either need to confirm the service entry (drop + meter) is able to support 200A. Of course you may be planning on replacing the whole service entry - in which case you probably already have it planned.
 
  #6  
Old 09-23-15, 12:20 PM
T
Member
Thread Starter
Join Date: Nov 2005
Location: canada
Posts: 187
Received 0 Upvotes on 0 Posts
Hi all thanks for the replies.

I think I will go with the panel linked below.

The meter is already a 200 amp but the feed in the mast is 1/0 aluminum so that's gotta go. (I think the power drop is 1/0 as well but from what I've read the power company is fine with that for 200 amp because it's outside. They can figure that part out on the reconnect)

I measured the conduit and it's only 1.5 inch so if I'm reading everything right I either have to replace the mast with 2 inch to use 4/0 aluminum or just pay a little more and use 2/0 copper in the existing mast? My plan is to have them do the disconnect in the morning and come back in the afternoon and I should be ready for them to reconnect. With time being a factor I think it would be much faster to just use the 2/0 copper.
 
  #7  
Old 09-23-15, 12:49 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
You are correct about the wire and conduit size. You may also need to upsize and modernize your grounding system as part of the service change, as the existing service probably does not have adequate grounding to meet code for 200A. The new service will need #4 copper to your primary grounding electrode (usually the water service entrance), and #6 copper to your secondary ground rod(s), and for any other bonding jumpers to metallic stuff like plumbing. If your mast goes through the roof and supports the service drop itself, the power company may want to see it replaced with 2" anyway for structural reasons. That is up to power company service installation standards. If the drop is lashed to an insulator lagged to the framing of the house and mast just contains the wire, 1.5" should be ok.
 
  #8  
Old 09-23-15, 12:57 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
Your power company may not reconnect without an inspection. Make sure to allow enough time for the inspector to see it and give you the sticker.
 
  #9  
Old 09-24-15, 09:53 AM
T
Member
Thread Starter
Join Date: Nov 2005
Location: canada
Posts: 187
Received 0 Upvotes on 0 Posts
The house is 3 story so the mast is just on the side with an insulator anchor.

PC Boss: Yes I looked into it already and you are correct I need the inspector to give it the thumbs up before I can energize the new panel. I'm going to wander into their office sometime next week and see about that. I'm hoping I can schedule hydro and the inspector right to get done in one day.

About the grounding: The ground rod has #6 and is in the ground a couple feet from the meter. As for primary the water line looks to have been replaced very recently with plastic/PEX. What are my options for another ground?
 
  #10  
Old 09-24-15, 03:19 PM
T
Member
Thread Starter
Join Date: Nov 2005
Location: canada
Posts: 187
Received 0 Upvotes on 0 Posts
NM. Looked into it. Locally (BC Canada) they want two ground rods 10 ft apart, 8 ft long and a number 6 copper continuous run.
 
 