Wiring for 230v table saw

Hi all,

I need to wire a new outlet for a table saw, and am getting conflicting advice on what I would need to do this. What wire and breaker should I be getting to support this job?

Here are the details
  • Running off a Sub-Panel
  • Saw Voltage: 230v
  • Saw HZ: 60hz
  • Saw Amp Draw: 13amps
  • Outlet will be 25' from fusebox

I forgot to mention that it needs a NEMA 6-15p receptacle.

Thanks
Steve
 

Last edited by steve_valet; 09-23-15 at 12:24 PM.
  #2  
Old 09-23-15, 12:11 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
  • 12-2 NM-b if cable or black, white, green, THHN #12 if conduit.
  • 20 amp two pole breaker or two 20 amp fuses.
  • NEMA 6-20 receptacle.
 

Last edited by ray2047; 09-23-15 at 01:52 PM.
  #3  
Old 09-23-15, 12:25 PM
S
Member
Thread Starter
Join Date: Sep 2015
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks ray2047! I totally forgot to mention that the saw currently requires a NEMA 6-15p receptacle (that's what's on the cord now). Does that change what you've advised?
 
  #4  
Old 09-23-15, 12:54 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Nope, a 6-20 has a "T" shaped slot that will accept either 15A or 20A plugs. You also should tape the white wire red to re-identify it as a hot conductor. If the cable is running through an area subject to damage, it needs to be protected by substantial wood framing, wallboard sheathing or sleeved in conduit. Generally the area under 8' high in a garage or shop is considered subject to damage.
 
  #5  
Old 09-23-15, 01:55 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
13 amps is close to the limit for a 15 amp circuit so I factored in a bit of head room especially since it is a motor and there is a a very brief high amp start current. Plug on the saw is fine for 13 amps.
 
 