Replacing electric range with gas range
Replacing old elecitric range in kitchen with gas range. The existing circuit is 40 amp with 8-4 nm-b cable. New range only requires 15 amps to power clock, light and gas ignitor. Can I simply install a 15 amp receptacle to the existing wiring and circuit? If so do I cut and cap the 4th wire since it us not required? Trying to avoid installing new circuit breaker and running new cable if possible.
#8
Member
Thread Starter
Join Date: Oct 2015
Posts: 5
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The microwave and range are located in an island in the middle of room. I designed the island to hide all electric within cabinets because it aligns with contemporary style of the overall kitchen design. Therefore the only b electric going to the island I can work with is the 20 amp circuit hidden with cabinet for microwave drawer.
#9
Then probably not code compliant. A 20 amp counter top receptacle circuit was required when built. You will need to add one now. Not Ideal but the existing cable can be used. I assume even though you wrote 8-4 it is 8-3, black, red, white, bare. (8-4 would also have a blue.)
At the island in a 4x4 box cap off the red. Connect #12 pigtails to the black white and bare. Connect the black and white pigtails to the line side of a 15* amp GFCI receptacle. Assuming the box is Metal using #12 pigtail the ground to both the GFCI and the box. (It is unlikely #8 will fit the GFCI receptacle so #12 pigtails are required.)
At the breaker panel remove the 40 amp 2-pole breaker and replace with a single pole 20 amp breaker and a fill plug for the remaining space in the panel cover. Cap the red wire. Using a #12 pigtail connect the black wire to the 20 amp breaker.** White and ground remain connected as before the change. (The neutral and bare fit the bus bar so no pigtail needed.)
*A 15 amp GFCI receptacle is normally used on a 20 amp circuit. Code permits that if two places to plug in and in residential use you are unlikely to have a 20 amp plug.
**A 20 amp breaker not a 15 amp breaker is used to meet the code requirement that was not met when the original wiring was done.
Note: The existing 20 amp circuit is not used due to code for fixed in place appliances which require a dedicated circuit.
At the island in a 4x4 box cap off the red. Connect #12 pigtails to the black white and bare. Connect the black and white pigtails to the line side of a 15* amp GFCI receptacle. Assuming the box is Metal using #12 pigtail the ground to both the GFCI and the box. (It is unlikely #8 will fit the GFCI receptacle so #12 pigtails are required.)
At the breaker panel remove the 40 amp 2-pole breaker and replace with a single pole 20 amp breaker and a fill plug for the remaining space in the panel cover. Cap the red wire. Using a #12 pigtail connect the black wire to the 20 amp breaker.** White and ground remain connected as before the change. (The neutral and bare fit the bus bar so no pigtail needed.)
*A 15 amp GFCI receptacle is normally used on a 20 amp circuit. Code permits that if two places to plug in and in residential use you are unlikely to have a 20 amp plug.
**A 20 amp breaker not a 15 amp breaker is used to meet the code requirement that was not met when the original wiring was done.
Note: The existing 20 amp circuit is not used due to code for fixed in place appliances which require a dedicated circuit.