Supply Wire Rating For Wall Fixture

Can I install a wall fixture requiring 75 degree C supply wire, using 600 Volt 12/2 NM-B romex rated for 90 degree C but with conductors rated for 60 degree C ampacity?
 
Sponsored Links
  #2  
Old 10-17-15, 06:56 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,058
I don't understand the last part of your question. No such thing as
conductors rated for 60 degree C ampacity?
The only conductors in the box would be the NM-b rated 90° and the fixture conductors which should be rated for at least 75°.
 
  #3  
Old 10-17-15, 07:17 AM
Member
Thread Starter
Join Date: Oct 2015
Posts: 2
ray2047....here is what I found on the spec for the wire.

Type NM-B (nonmetallic-sheathed cable) may be used for both exposed and concealed work in normally dry locations at temperatures not to exceed 90˚C (with-Ampacity limited to that for 60˚C conductors) as specified in the NEC 1.

I am confused by the 60˚C conductors as stated above when the fixture indicates that it needs 75˚C supply wire??

Thanks for helping out!
 
  #4  
Old 10-17-15, 07:26 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,058
That just means older NM-b was rated for 60°and newer NM-b wire is rated for 90° but when they changed the temperature specification they didn't change the maximum amps the wire could handle. Maximum amps for #14 is 15 amps regardless of if it is older 60° wire or newer 90°wire.
 