Help with box fill calculation
Old 10-23-15, 02:05 PM
C
I was wondering if someone could help me with a box fill calculation. I have a 1-gang NM box (Carlon 18 cu. in.). There are 4 - 12 gauge cables that terminate in it. There is also a 3-way switch. I am concerned that it is overfilled. From my calculation, it appears that there should be at least a 22.5 cu. in. box. Is that correct? Do they even make a 1-gang box that large? I appreciate any input.
Old 10-23-15, 02:37 PM
I
Received 43 Votes on 41 Posts
You have:
8 conductors entering and exiting (maybe more if any of those cables are 12-3)
1 conductor to represent all grounds
2 conductors to represent the device (switch)
11 conductors * 2.25 cu/in for #12 wire = 24.75 cu in minimum box size
There may be some speciality boxes out there greater than 22.5, but that is the largest "deep" single gang box commonly available. I'd say you need a 2 gang box in that spot.
Old 10-23-15, 02:49 PM
ray2047's Avatar
Received 13 Votes on 11 Posts
If it is a new installation they make a two gang box where half is covered by the Sheetrock.
Edit: More research thanks to PCBoss shows the box I was refering to is only 17 cubic inches so... never mind.
Last edited by ray2047; 10-23-15 at 10:07 PM. Reason: Removed possibly incorrect information.
Old 10-23-15, 09:53 PM
pcboss's Avatar
Received 92 Votes on 79 Posts
I believe the box ray linked to is a 17 inch box based on the part number.
Old 10-23-15, 09:58 PM
ray2047's Avatar
You are correct. I missed that.
Old 10-23-15, 10:15 PM
pcboss's Avatar
B 117 = 1 gang, 17 cubic inch.
Old 10-28-15, 05:58 AM
A
Received 17 Votes on 17 Posts
This program may be of help also for figuring box fill calculations.