What size wire do I need for a 100 amp subpanel I will be about 50 foot between main and subpanel.

Thank You
 
Sponsored Links
  #2  
Old 11-04-15, 10:02 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,041
For a 60A panel--- Three #6 and one #10. .
 

Last edited by ibpooks; 11-05-15 at 08:31 AM. Reason: Note added
  #3  
Old 11-05-15, 08:30 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,502
What wiring method do you want to use? Cable, conduit, indoors, outdoors, aluminum, copper?
 
  #4  
Old 11-05-15, 08:26 PM
Member
Thread Starter
Join Date: Nov 2015
Posts: 5
Copper run in conduit outdoors don't know if I even know if I need 100 amp breaker I do have a 100 amp sub panel but it is just a bedroom with 2 15 amp breakers to run 7 plug and two lights and a 20 amp breaker for a 110 8000 btu window unit.
 
  #5  
Old 11-06-15, 08:11 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,502
You can feed the panel with up to 100A, but can be less. For the small cabin you describe a much smaller feed would be acceptable. Even 40A would do it. Potentially even a 20A multiwire circuit could do without a panel. Will there also be an electric heater in addition to the AC unit?

For 100A if you did choose to go that way you would need #3 THHN copper for the hots and neutral and #8 green for the ground in at least 1-1/4" conduit.

If you go with 60A, which is the next common size down, you can use #6 THHN copper for the hots and neutral and #10 green for the ground. Technically you could use 3/4" conduit, but I wouldn't go below 1".

For 40A or 50A go with #8 THHN copper for the hots and neutral and #10 green for the ground.

In any case burial depth for the PVC conduit is 18"
 
  #6  
Old 11-06-15, 06:19 PM
Member
Thread Starter
Join Date: Nov 2015
Posts: 5
yes there will be a electric heater thinking about a 1500 watt baseboard heater
 
  #7  
Old 11-06-15, 06:59 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,379
60 amps is more than adequate for the load.
 