100 AMP Sub Panel
Old 11-04-15, 08:02 PM
100 AMP Sub Panel
What size wire do I need for a 100 amp subpanel I will be about 50 foot between main and subpanel.
Thank You
Old 11-04-15, 09:02 PM
ray2047's Avatar
For a 60A panel--- Three #6 and one #10. .
Old 11-05-15, 07:30 AM
What wiring method do you want to use? Cable, conduit, indoors, outdoors, aluminum, copper?
Old 11-05-15, 07:26 PM
Copper run in conduit outdoors don't know if I even know if I need 100 amp breaker I do have a 100 amp sub panel but it is just a bedroom with 2 15 amp breakers to run 7 plug and two lights and a 20 amp breaker for a 110 8000 btu window unit.
Old 11-06-15, 07:11 AM
You can feed the panel with up to 100A, but can be less. For the small cabin you describe a much smaller feed would be acceptable. Even 40A would do it. Potentially even a 20A multiwire circuit could do without a panel. Will there also be an electric heater in addition to the AC unit?
For 100A if you did choose to go that way you would need #3 THHN copper for the hots and neutral and #8 green for the ground in at least 1-1/4" conduit.
If you go with 60A, which is the next common size down, you can use #6 THHN copper for the hots and neutral and #10 green for the ground. Technically you could use 3/4" conduit, but I wouldn't go below 1".
For 40A or 50A go with #8 THHN copper for the hots and neutral and #10 green for the ground.
In any case burial depth for the PVC conduit is 18"
Old 11-06-15, 05:19 PM
yes there will be a electric heater thinking about a 1500 watt baseboard heater
Old 11-06-15, 05:59 PM
CasualJoe's Avatar
60 amps is more than adequate for the load.