wiring a floor outlet


  #1  
Old 11-06-15, 12:11 PM
T
Member
Thread Starter
Join Date: Mar 2015
Location: usa
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
wiring a floor outlet

I've installed a floor outlet and now need to connect to a power supply.
Under the house is an outlet into which the main furnace is plugged, yellow Romex in and out.
Can I run my floor outlet wires to this box? If so, would type NM-B, 14/2 white wire rating be sufficient?
 

Last edited by trailsprinter; 11-06-15 at 12:52 PM.
  #2  
Old 11-06-15, 12:35 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
No, code requires the central heating system be wired on a dedicated circuit. You would need to find power from another circuit or run a new one from the panel.
 
  #3  
Old 11-06-15, 01:32 PM
T
Member
Thread Starter
Join Date: Mar 2015
Location: usa
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
There is currently a fluorescent lighting fixture that is wired into this furnace box. Was that connected incorrectly? (not me, I bought the house this way).

BTW, thanks for the helpful reply!
 
  #4  
Old 11-06-15, 01:44 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Probably incorrect from a previous occupant, yes. If this is a much older home it may have been installed prior to the code going in effect.

FYI, yellow romex is almost always #12. If a circuit is wired from the panel with #12, the whole thing needs to be at least #12. You can "upsize", (e.g. add #12 to a #14 circuit), but you cannot "downsize" (e.g. add #14 on a #12 circuit).
 
  #5  
Old 11-06-15, 03:06 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
Older #12 was also white. The color is not a reliable gauge of wire size.
 
  #6  
Old 11-06-15, 05:42 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
Under the house is an outlet into which the main furnace is plugged, yellow Romex in and out.
This is a little off topic, but I think it needs to be mentioned here. The furnace really shouldn't be plugged in, but should be hardwired to a dedicated circuit. IF it is plugged in, as you say it is, the receptacle needs GFCI protection.
 
 