240 volt 3 prong female plug to a 240 volt 4 prong male twist type connector

Own a vintage 155 Lincoln MIG welder, with a 3 prong 240 male plug that I would like to use with my generator. The generator does not have a corresponding receptacle and would it be possible to swap out the plug on the MIG welder for a plug that corresponds with the receptacle on the generator? If so, I purchased a 10 foot, extremely heavy gage extension cord that match the plug on the MIG welder and rather than swap out the plug on the welder would it be possible to swap the plug on the extension cord? If it can be done, would the there be a significant voltage loss due to the gage and length of cord??

Existing Plug:
http://ecx.images-amazon.com/images/...L._SL1289_.jpg

Replacement Plug:
http://ecx.images-amazon.com/images/...L._SL1302_.jpg

Due to the size of the cords I would have an electrician change the connector.

Comments/Suggestions appreciated.
 
Sponsored Links
  #2  
Old 11-08-15, 03:14 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
What gauge is the extension cord? How many amps does the welder draw? What is the output rating of the twist lock receptacle on the generator?
 
  #3  
Old 11-08-15, 03:50 PM
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 290
Received 0 Votes on 0 Posts
Extension cord: 8/3. The spec plate on the Lincoln 155, 20 amp @ 230V. Generator twist lock outlet 240 volts 30 Amps. Interested if the current combination of cords-amp-output is sufficient, although, currently searching for generator that puts out minimum of 10K watts.
 
  #4  
Old 11-08-15, 05:12 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
The cord size is. Cord is rated for 40 amps under normal service but could handle more then that when used for a welder depending on the duty cycle of the welder.
Due to the size of the cords I would have an electrician change the connector.
No need for that. It is easy to do. We can walk you through it. Please post a picture of the cord you actually bought and the two ends.
 
  #5  
Old 11-09-15, 10:44 AM
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 290
Received 0 Votes on 0 Posts
Cable did not want to cooperate in attempting a photo shoot, pic's of the female end did not come-out, if additional photo's are needed let me know?

In terms of an electrician, thought due to the size of the individual wire strains a special crimping, or similar tool, would be required?

Thank you for the information:
 
Attached Images     
  #6  
Old 11-09-15, 11:06 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
thought due to the size of the individual wire strains a special crimping, or similar tool, would be required?
No, it would be screws.

Plug below is for illustration only. There would be no wire connected to the silver screw for your application. Only wires to the two brass screws and the ground.

Name:  solarcamperwire14.jpg
Views: 11213
Size:  40.0 KB

Name:  4-prong-l14-30r.gif
Views: 6279
Size:  6.8 KB
 

Last edited by ray2047; 11-09-15 at 11:34 AM.
  #7  
Old 11-09-15, 11:46 AM
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 290
Received 0 Votes on 0 Posts
ray2047,

Can't thank you enough, pic's, and all; especially the 'how to' connect the 3 wires to the 4 prong plug. Intend buying the plug tomorrow at the hardware store, I probly should remove the 3 prong male plug and pull back the insulation to determine the gage wire, not sure if the replacement plug come in different sizes for the large gage wire. I am not that knowledgeable but from the pic's and information I should be able to swap plugs and save the cost of an electrician.

Again, thank you
 
  #8  
Old 11-09-15, 12:34 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
The plugs should take #8 but check. You said the cord you had was 8-3.
 
  #9  
Old 11-09-15, 02:43 PM
Member
Thread Starter
Join Date: Jun 2011
Location: USA
Posts: 290
Received 0 Votes on 0 Posts
Found a couple web-sites where customers ask similar question and appears 10 is the largest gauge recommended. Although I would like to put the 3-8 extension cord to use, I can swap the male connector on the MIG power cord, which is around 5' long and 3-10.

Thank you!!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: