Light circuit lost voltage


  #1  
Old 11-17-15, 11:30 AM
S
Member
Thread Starter
Join Date: May 2009
Location: u.s.
Posts: 141
Upvotes: 0
Received 1 Upvote on 1 Post
Light circuit lost voltage

I have a motion detector light at the back of my house. It has not worked in years. At one time I remember it coming on but not anymore. I can not find a switch in the house for it and so I assume it is direct wired. I want to install a new light now. I removed the old light and checked the voltage. It reads 1.5 volts. WTH?!?!
Any idea whats going on here? All the other things on the same circuit work fine.
 
  #2  
Old 11-17-15, 12:10 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Just do double check do you have any mystery switches which you don't know what they do? Does the light have just a single 2-conductor cable. Did you measure both hot to ground and hot to neutral? Is this light on a wall with the inside finished or an unfinished attic gable?
 
  #3  
Old 11-17-15, 12:19 PM
S
Member
Thread Starter
Join Date: May 2009
Location: u.s.
Posts: 141
Upvotes: 0
Received 1 Upvote on 1 Post
There is a ground wire coming out of the wall which is attached to the crossbar that the light screws to. The other 2 wires coming out of the wall were attached to the fixture, and they are black and white. These measure 1.5 volts.
We do have a mystery switch but it has no effect. I will check voltage again tomorrow with this switch in the other direction. Either way, 1.5 volts with a switch on or off is a defect, isn't it?
 
  #4  
Old 11-17-15, 12:27 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Probably a defect in your meter or the way you're using it. What you're seeing is likely a phantom voltage reading. If you measure the voltage with a load in parallel it will read zero. An analog meter or neon bulb tester makes this more obvious than a consumer-grade digital meter.
 
  #5  
Old 11-17-15, 01:15 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
There is a ground wire coming out of the wall
What is the voltage between ground and black.
 
  #6  
Old 11-18-15, 10:57 AM
S
Member
Thread Starter
Join Date: May 2009
Location: u.s.
Posts: 141
Upvotes: 0
Received 1 Upvote on 1 Post
As I said, black to white measures 1.5 v. I just went out to check measurements to ground. White to ground measures 155v and black to ground measures 1.5v. This is really rediculous because it should be a 110v circuit.

As far as I can tell, all other items on this circuit are working fine.
 
  #7  
Old 11-18-15, 11:01 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,078
Received 3,422 Upvotes on 3,068 Posts
You have lost your neutral connection. White/neutral to ground should be 0v.
 
  #8  
Old 11-18-15, 11:03 AM
S
Member
Thread Starter
Join Date: May 2009
Location: u.s.
Posts: 141
Upvotes: 0
Received 1 Upvote on 1 Post
Where is the 155v on the white/ground coming from?
 
 