100 amp sub panel. what do i need to do for wire?
#1
Member
Thread Starter
Join Date: May 2015
Location: usa
Posts: 9
Received 0 Votes
on
0 Posts
100 amp sub panel. what do i need to do for wire?
i have 200 amp main in basement. what i'd like to do is just drill holes through my joists and out into the garage to 100 amp sub in attached garage. so i guess what i am wondering is what wire can i use for this? i'd rather not run it in conduit if i don't have too. it will be a finished basement.
#2
Why do you think you need a full 100 amps in the garage? Is the subpanel rated at 100 amps? I wouldn't install more than a 60 amp circuit with 6-3 NM-B cable to the subpanel fed from a 60 amp 2 pole breaker in the basement main panel and that would be gobs of power for any garage.
#3
Member
Thread Starter
Join Date: May 2015
Location: usa
Posts: 9
Received 0 Votes
on
0 Posts
i more then likely don't need 100 amps. i have the 100 amp panel i'd like to wire it for 100 amps. i have a few things out there that will draw some power. it will also feed my cloths dryer. your idea for the 60 amp circuit would more then likely work. i'm just wondering how much more $ and trouble the 100 amp would be. so i just need to know if there is a wire i can use inside in this application.
#4
For a full 100 amps I would install 1 1/4" conduit and use 3 - #3 copper conductors and 1 - #8 ground, but you wanted to run cable. My first cable choice would be 2-3 NM-B cable, if you can find it or #1 aluminum SER cable. These cables would be pretty difficult to pull through holes bored in the joists.
#5
Member
Thread Starter
Join Date: May 2015
Location: usa
Posts: 9
Received 0 Votes
on
0 Posts
thanks, i want to finish the basement and don't want to see the conduit on the bottom of the joists.
unless you're saying you'd put the conduit in the joists. that seems like it'd be harder then pilling wire, and i'm not even sure you can do that? am i missing something there?
unless you're saying you'd put the conduit in the joists. that seems like it'd be harder then pilling wire, and i'm not even sure you can do that? am i missing something there?
#6
I agree with Joe, you should definitely consider running a 60A feeder. Wire is pretty expensive and the larger gauges are even more difficult to run. A 60A garage subpanel is likely more than enough for a well-furnished one or two-person shop.
I installed a 100A subpanel in a basement and dealing with the Al feeder cable was like wrestling a python (or at least what I'd imagine wrestling a python would be like). There was no way that cable was going through any bored holes, it was hard enough to just get it attached to the bottom of the joists. Copper would of course be a bit easier and downgrading to 6ga wire.
I installed a 100A subpanel in a basement and dealing with the Al feeder cable was like wrestling a python (or at least what I'd imagine wrestling a python would be like). There was no way that cable was going through any bored holes, it was hard enough to just get it attached to the bottom of the joists. Copper would of course be a bit easier and downgrading to 6ga wire.
#7
If you have a helper to unroll the cable correctly and if you use hole saws or a decent size forstner bit to bore the joists, you can pull SER cable through framing. You can't make any tight corners -- at least a 1' radius or so will be required. The #1 aluminum SER for 100A will probably be about the same cost as #6 copper for 60A, but it will be more work to install.
#10
and out into the garage to 100 amp sub in attached garage....it will also feed my cloths dryer
#11
Member
Thread Starter
Join Date: May 2015
Location: usa
Posts: 9
Received 0 Votes
on
0 Posts
attached,
i am ok with the added cost for the 100 amp breaker. alum looks like its not really that spendy. i should be able to get a few people to help my wrestle it through...
i am ok with the added cost for the 100 amp breaker. alum looks like its not really that spendy. i should be able to get a few people to help my wrestle it through...