My service panel ground wire broke.


  #1  
Old 12-12-15, 08:49 AM
F
Member
Thread Starter
Join Date: Dec 2004
Location: mobile alabama USA
Posts: 130
Upvotes: 0
Received 0 Upvotes on 0 Posts
My service panel ground wire broke.

I was doing some construction very near service panel ground wire and I was going to dig it up temperarily and rebury it but it's very old and it broke above ground. Can I ust get a conector of some sort and rejoin the 2 pieces or what? Thanks.
 
  #2  
Old 12-12-15, 09:05 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,515
Upvotes: 0
Received 276 Upvotes on 252 Posts
You can temporarily patch it together but technically you need a continuous ground wire from the panel to one ground rod. (The run(s) to additional ground rod(s) can be spliced on.)
 
  #3  
Old 12-12-15, 09:11 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
You can use a polaris or split lug bug for a temporary repair. Home improvement stores will have the split lug type which are less costly.

Name:  polaris.jpg
Views: 699
Size:  13.0 KB
 
  #4  
Old 12-12-15, 05:11 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,499
Received 92 Upvotes on 84 Posts
For a permanent fix you are supposed to be able to use an irreversible compression splice.
something like: Burndy YGS6C Hylink Grounding Irreversible Compression Splice, #6 sol./str. Copper Conductor Size, 2.38" Length: Terminals: Amazon.com: Industrial & Scientific
 
 