Self grounding/bonding switches


  #1  
Old 12-10-15, 10:13 AM
B
Member
Thread Starter
Join Date: Jan 2011
Location: Hennepin County, MN, USA
Posts: 123
Upvotes: 0
Received 0 Upvotes on 0 Posts
Self grounding/bonding switches

I have some busy 2gang metal boxes. If I can save grounding the Legrand CSB20ac switches it would be nice. When I ground the box, and if I remove the paper washer from the yolk do I need to have a grounding pigtail from these switches?
 
  #2  
Old 12-10-15, 10:40 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
if I remove the paper washer from the yolk do I need to have a grounding pigtai
the paper washer is only to retain the screw. A special switch is required for it to be self grounding. Removing the washer doesn't do anything. However if the box is metal and properly grounded grounding the the switch is optional if the cover plate is non metallic.
 
  #3  
Old 12-10-15, 10:44 AM
B
Member
Thread Starter
Join Date: Jan 2011
Location: Hennepin County, MN, USA
Posts: 123
Upvotes: 0
Received 0 Upvotes on 0 Posts
I will have a metal cover plate. But doesn't the metal to metal contact of the box, switch and cover plate suffice? It means 5 instead of 7 ground wires in the box.
 
  #4  
Old 12-10-15, 10:51 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
You may need to install a deeper box if the exceeds box fill.
 
  #5  
Old 12-10-15, 10:53 AM
B
Member
Thread Starter
Join Date: Jan 2011
Location: Hennepin County, MN, USA
Posts: 123
Upvotes: 0
Received 0 Upvotes on 0 Posts
Can't go with deeper boxes, it is on an ICF concrete wall.

But doesn't the metal to metal contact of the box, switch and cover plate suffice? It means 5 instead of 7 ground wires in the box.
 
  #6  
Old 12-10-15, 10:54 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
I'm surprised the Legrand heavy duty switches aren't self-grounding, but I don't see any mention of it on the spec sheet. A self-grounding switch will either have a small copper plate or a pair of steel wires pinching the mounting screw to the device yoke. You can still save a lot of space by cutting one long ground wire and looping from switch to switch, then terminate it at a ground screw in the back of the box.

Or change to Leviton TradeMaster switches which are spec'd as self-grounding.

All grounds combined count toward one box fill unit, doesn't matter how many devices they touch. Pigtails inside the box don't count toward box fill.
 
  #7  
Old 12-10-15, 03:05 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
Can't go with deeper boxes, it is on an ICF concrete wall.
What kind of box is it? Is it a surface mounted steel 1900 box with a steel 1900 raised cover?
 
  #8  
Old 12-10-15, 03:36 PM
B
Member
Thread Starter
Join Date: Jan 2011
Location: Hennepin County, MN, USA
Posts: 123
Upvotes: 0
Received 0 Upvotes on 0 Posts
  #9  
Old 12-10-15, 03:59 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
That box is a 2-gang handy box and the wrong box to use in my opinion. You didn't say, but assuming it's surface mounted, what you should have used is a 1900 box (4" square) with a raised cover. The devices actually have a bolted connection to the raised cover and as long as the box is properly grounded, it isn't necessary to connect a ground pigtail to the devices because the raised cover screws tightly to the box. 2-gang handy boxes are something I have never seen at a supply house. The first one I ever saw was just a couple years ago at a box store.

https://www.google.com/search?q=1900...HdNqAZkQsAQIOg

https://www.google.com/search?q=1900...HUxnCIkQsAQIIw
 
  #10  
Old 12-10-15, 04:11 PM
B
Member
Thread Starter
Join Date: Jan 2011
Location: Hennepin County, MN, USA
Posts: 123
Upvotes: 0
Received 0 Upvotes on 0 Posts
With the mud ring, raised cover the 1900 is too deep. I am using EIFS only about 1/8" thick. I used the handy boxes recessed in the EPS of the ICF that is 2.5" thick.
 
  #11  
Old 12-10-15, 04:23 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
I am using EIFS only about 1/8" thick. I used the handy boxes recessed in the EPS of the ICF that is 2.5" thick.
Not sure what all that stuff is, but if you had used a 1 1/2" deep 1900 box the raised cover wouldn't have made the entire installation over 2". If it's all surface mounted I don't see an issue with the depth anyway. You don't use a mud ring when using a raised cover.
 
  #12  
Old 12-10-15, 05:14 PM
B
Member
Thread Starter
Join Date: Jan 2011
Location: Hennepin County, MN, USA
Posts: 123
Upvotes: 0
Received 0 Upvotes on 0 Posts
The boxes are flush mounted in the 2.5" of expanded poly styrene of the Insulated Concrete Form.
I don't see the point in using a two piece 4" 1900 box. When the handy box can do it in one piece. Also with a raised cover you can't use a regular plate, that would extend beyond the edge of the box for a cleaner looking install.
 
  #13  
Old 12-11-15, 09:03 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
The boxes are flush mounted in the 2.5" of expanded poly styrene of the Insulated Concrete Form.
You never said all that before. Go ahead and do it your way then.

I don't see the point in using a two piece 4" 1900 box. When the handy box can do it in one piece. Also with a raised cover you can't use a regular plate,
As a FYI, You don't use a plaster ring when using a raised cover, the 1900 box is just one piece. The devices bolt to the raised cover and the raised cover is solidly screwed to the box. You also cannot use a regular plate over a raised cover. What would be the point anyway? Raised covers are typically used when the 1900 box is surface mounted on a concrete or masonry wall.
 
  #14  
Old 12-11-15, 12:31 PM
B
Member
Thread Starter
Join Date: Jan 2011
Location: Hennepin County, MN, USA
Posts: 123
Upvotes: 0
Received 0 Upvotes on 0 Posts
I did say, twice, that the boxes were recessed into 2.5" of eps. Nor did I ever want to use a raised cover or mud ring, or a different box. My question was about self grounding switches, not boxes. http://images.ibsrv.net/ibsrv/res/sr...ilies/wall.gif (red-faced head hitting brick wall)


I bought those switches a few months ago, and the new version have a little metal tab clinging to one of the screws. FYI I installed the switches I had, no ground wire. I am confident they will ground through the metal box.
 
  #15  
Old 12-11-15, 03:32 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,754
Received 672 Upvotes on 570 Posts
A switch that is attached to a grounded metal box, with metal screws, is considered grounded. 404.9(B) (2011)

Just recently I have started to see switches with a self grounding clip installed similar to the ones on self grounding receptacles. I do not know if this is a future code requirement (2017) or a requirement of UL.
 

Last edited by Tolyn Ironhand; 12-11-15 at 03:51 PM.
 