ground rod

An electrician added an additional ground rod to my house to bring it up to code. After several failed attempts to drive it straight down (hitting ledge at 4")he gave up and drove the rod at a shallow angle. My guess is that the rod is only 1-2 feet deep. Is this acceptable?
 
Sponsored Links
  #2  
Old 12-13-15, 01:00 PM
Member
Join Date: Jan 2011
Location: USA
Posts: 4,438
Received 25 Votes on 21 Posts
No and he should have known better then that.
How far out from the foundation was he trying to drive it.
He may have hit the footing it he was not out far enough.
 
  #3  
Old 12-13-15, 01:31 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
You can drive ground rods at 45 or dig a trench and bury them horizontally.
 
  #4  
Old 12-13-15, 06:51 PM
Member
Thread Starter
Join Date: Mar 2007
Posts: 1,422
Received 10 Votes on 9 Posts
He was not hitting the footers. It's NH and he was hitting granite. I thought going in at an angle was a better idea than my suggestion of just cutting the rod off at 4'.

Not that I'm planning on moving anything, but how deep would the trench have to be?
 
  #5  
Old 12-13-15, 07:36 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
NEC Article 250:
3. The electrode shall be installed such that at least 8 feet of length is
in contact with the soil. It shall be driven to a depth of not less than 8
feet except that, where rock bottom is encountered, the electrode shall be
driven at an oblique angle not to exceed 45 degrees from the vertical or
shall be buried in a trench that is not less than 2-1/2 feet deep.
The upper
end of the electrode shall be flush with or below ground level unless the
aboveground end and the grounding electrode conductor attachment are
protected against physical damage as specified in Section 250-10."
Highlight added by me.
 
  #6  
Old 12-13-15, 08:28 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,913
Received 24 Votes on 20 Posts
Do not cut the rod. You need 8' of direct earth contact minimum. The top needs to be flush or below the surface.
 
  #7  
Old 12-14-15, 06:35 AM
Member
Thread Starter
Join Date: Mar 2007
Posts: 1,422
Received 10 Votes on 9 Posts
Sorry. The "cut the rod" comment was intended as a joke. I should have added one of those smiley thingys. It was not cut but I'm sure that it exceeds the 45* angle.
 
  #8  
Old 12-14-15, 07:03 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
When the geology is all rock there's only so much you can do. Code specifies 30" deep for horizontal rods, but it sounds like that might even be a significant challenge if you have solid granite at 48". The best solution is simply to add additional ground rods at whatever depth or angle you can feasibly achieve.
 
  #9  
Old 12-14-15, 04:21 PM
Member
Thread Starter
Join Date: Mar 2007
Posts: 1,422
Received 10 Votes on 9 Posts
Thanks Ben for some common sense advice. My electrician is a good guy and he knows we're prepping this house to sell. I am 100% positive that he would do nothing to jeopardize that. My questions were as much out of curiosity than anything else - like wondering what would you do if your house is sitting on surface rock?

I've done a little reading and I know the <25 ohm ground requirement but how/where is that measured?
 
  #10  
Old 12-14-15, 04:56 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,668
Received 340 Votes on 318 Posts
I've done a little reading and I know the <25 ohm ground requirement but how/where is that measured?
That IS the question.

You would normally measure between the ground rod and a known good ground. A known good ground would be a metal water service if you have city water.

The ground rod would not be connected to the service during the testing.
 
  #11  
Old 12-14-15, 06:40 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,913
Received 24 Votes on 20 Posts
The testing equipment takes time and is expensive. It is normally easier to drive a second rod and be done with it.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: