Breaker size
Old 12-17-15, 10:29 PM
Breaker size
Good day,
I have a 400kw, 230V, 3 phase Air cooled Chiller. What size of breaker should i use? I come up with too large numbers. Can you show me how you come up with your answer if you have?
Old 12-17-15, 10:49 PM
There should be an ID plate on the unit listing all the specs.
Old 12-17-15, 10:54 PM
This was only given to me sir. He said that the unit of the chiller has 400 KW, 230V, 3P, 60 HZ.
Old 12-18-15, 12:20 AM
You're talking about a HUGE load. You cannot guess at the breaker size. The equipment manufacturer specifies the requirements.
As a basic answer... 400,000w / 230v = 1740 amps / 3ph = 580amps.
This is just a rough estimate. Based on powering a chiller.... you'd need approx a 700A breaker.
It's extremely rare to find this large of a chiller operating on 230v.
Power in your area.... Single phase 115/230 3-phase 240/480 60hz.