Breaker size

Good day,

I have a 400kw, 230V, 3 phase Air cooled Chiller. What size of breaker should i use? I come up with too large numbers. Can you show me how you come up with your answer if you have?
 
Sponsored Links
  #2  
Old 12-17-15, 09:49 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,459
There should be an ID plate on the unit listing all the specs.
 
  #3  
Old 12-17-15, 09:54 PM
Member
Thread Starter
Join Date: Aug 2015
Location: Philippines
Posts: 77
This was only given to me sir. He said that the unit of the chiller has 400 KW, 230V, 3P, 60 HZ.
 
  #4  
Old 12-17-15, 11:20 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,459
You're talking about a HUGE load. You cannot guess at the breaker size. The equipment manufacturer specifies the requirements.

As a basic answer... 400,000w / 230v = 1740 amps / 3ph = 580amps.
This is just a rough estimate. Based on powering a chiller.... you'd need approx a 700A breaker.

It's extremely rare to find this large of a chiller operating on 230v.
Power in your area.... Single phase 115/230 3-phase 240/480 60hz.
 