I am currently working on some "upgrades" to one of the rooms in my house. Something as simple as adding 1 light has turned into a rather large project. For whatever reason half the house seems to be wired together.

To sum it up, I've pulled and re-ran half of the wiring but never touched the source. The line from the Panel is 12-3. I haven't pulled the breakers to look to see how the 12-3 is attached, but I assume the 12-3 is coming off of two different twin breakers. When I flip one of the breakers on, everything works fine. As soon as I flip the other, it blows both. I assume the black is off of one breaker and the red is off the second breaker, but not sure.

I've attached a rough outline of the wiring path and the breaker that is tripping. Breaker #27 is the one that is currently on and working. Breaker #26 is the one that blows both 26 and 27 when it is flipped on. Any idea's on what may be happening?



 
Sponsored Links
  #2  
Old 12-20-15, 10:18 PM
J
Member
Thread Starter
Join Date: Apr 2015
Location: USA
Posts: 38
Received 0 Votes on 0 Posts
Aren't those twin/tandem?
 
  #3  
Old 12-20-15, 10:19 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 58,577
Received 1,042 Votes on 966 Posts
You are working with multiwire branch circuit. The three wire connects the panel to the junction box. At the junction box the circuit is split up. One circuit is red and white. The other circuit is white and black.

It is very important that the neutral/white connection be very solid. If your circuits lose the neutral connection you could get up to 240v on a 120v receptacle. This would cause damage to any connected devices.

Ray..... he means two and three wire.
 
  #4  
Old 12-20-15, 10:22 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
To avoid confusion I have deleted my post.
 
  #5  
Old 12-20-15, 10:25 PM
J
Member
Thread Starter
Join Date: Apr 2015
Location: USA
Posts: 38
Received 0 Votes on 0 Posts
You are working with multiwire branch circuit. The three wire connects the panel to the junction box. At the junction box the circuit is split up. One circuit is red and white. The other circuit is white and black.
So then basically at the junction box, I can take half of what's connected and put it on the red/white side, and the rest will go on the black/white side.
 
  #6  
Old 12-20-15, 10:30 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 58,577
Received 1,042 Votes on 966 Posts
Yes.... that's how the circuiting works. Like I mentioned.... make sure you make a very good neutral splice. You do not want that to open.
 
  #7  
Old 12-20-15, 10:36 PM
J
Member
Thread Starter
Join Date: Apr 2015
Location: USA
Posts: 38
Received 0 Votes on 0 Posts
Thanks for the help.

In its current state, live off of the one breaker, will this be ok until the morning, or do I need to head up there and change this now?
 
  #8  
Old 12-20-15, 11:24 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 58,577
Received 1,042 Votes on 966 Posts
The two circuits can be run independent of each other.

What you need to locate tomorrow is where you've connected the red and black.
The circuit will be ok until tomorrow.
 
  #9  
Old 12-21-15, 08:06 AM
J
Member
Thread Starter
Join Date: Apr 2015
Location: USA
Posts: 38
Received 0 Votes on 0 Posts
Well provided nothing comes loose, it looks like everything is ok. I found the black/red error and separated them. Getting the six #12 neutrals was a challenge though. Not much room for forgiveness on the wire lengths.

Thank you again for the help.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: