This cable connects my electric cooktop to my electrical panel (on a 30 amp breaker). I'd like to replace the cooktop with an electric range (oven and cooktop in one.)

I have two questions:

1) What gauge is this cable?
2) What size cable and breaker do I need for the range?

Attachments:
a) picture of the cable that feeds the current cooktop
b) picture of the nameplate for the new (used) range

Any help would be appreciated.
 
Attached Images   
  #2  
Old 12-23-15, 03:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,081
Received 3,422 Upvotes on 3,068 Posts
Can't read the tag.... what is the wattage at 240vac ?

That is 8-2 aluminum cable. To be code compliant now it needs to be three wire with ground and for a unit your size it should be 8-3 NM W/ground.

If the range is 10.5 kw at 240v .... you're looking at a 44A load.
 
  #3  
Old 12-23-15, 04:58 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Is that SE by any chance copper?
 
  #4  
Old 12-23-15, 05:26 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
Check the breaker size now. A new stove is going to need at least a 40 amp circuit.
 
  #5  
Old 12-23-15, 05:48 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,081
Received 3,422 Upvotes on 3,068 Posts
The OP stated now connected to 30A breaker. That's why I assumed aluminum SE cable.
 
  #6  
Old 12-23-15, 06:45 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,787
Received 173 Upvotes on 156 Posts
Judging by the cable sheath, I think it is old copper SE cable. I would replace it with the 8-3 NM-B cable too and use a 40 amp breaker.
 
  #7  
Old 12-23-15, 08:38 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
The cable sheath DOES have type SE printed on it. Whether it is copper or aluminum I have no idea.
 
  #8  
Old 12-24-15, 05:57 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
If it is an EXISTING branch circuit to the range the SE would be fine if it's 8 CU.
 
  #9  
Old 12-24-15, 07:14 AM
L
Member
Thread Starter
Join Date: Sep 2010
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks all for your help...

Here's a better picture of the stove nameplate. Yes, 10.5 kw at 240v.

If I'm looking at a 44 amp load, then I need a 50 amp breaker, right? Will the 8 gauge cable suffice?

Name:  stove.jpg
Views: 1198
Size:  19.3 KB
 
  #10  
Old 12-24-15, 07:18 AM
L
Member
Thread Starter
Join Date: Sep 2010
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
I think it is copper. Two copper conductors with a braided aluminum ground (as I recall; it's been a while since I was in the junction box...)

So I know there are "preferences", but I'm trying to figure out what code requires. For this stove, would 8 gauge and 40 amp breaker be adequate? I would really, really like to not have to pull new cable, but I will if it's unsafe.
 
  #11  
Old 12-24-15, 08:22 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
If the insulated conductors are copper the other conductor will be copper also.
 
  #12  
Old 12-24-15, 08:22 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,471
Received 83 Upvotes on 75 Posts
Code is 8 gauge copper is good for 40 amps so technically you need to run a new 6/3 cable and a 50 amp breaker. Reality is that the range will work fine until you have all burners on at the same time as the oven and it pops the 40 breaker after running for an hour.

If aluminum the circuit it is only good for 30 amps and your current breaker is properly sized.
 
  #13  
Old 12-24-15, 09:08 AM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
I am not experienced enough to identify the cable type just by the designation, so I need help on if the cable has an insulated neutral, not a bare ground.

IF you have an insulated neutral, and it's copper cable, this installation is most likely grandfathered.
You must ensure the bonding strap was not removed though.

A typical installation would be a 40 amp breaker.
 
  #14  
Old 12-24-15, 10:51 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
If I'm looking at a 44 amp load, then I need a 50 amp breaker, right? Will the 8 gauge cable suffice?
No it will not. You need a 50 amp breaker. That pretty well makes it moot. You need 6-3 NM-b. Since you are running new cable I'd suggest installing a receptacle and adding a cord set to the stove.
 
  #15  
Old 12-24-15, 10:54 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Its SE so it is a braided bare neutral.
 
  #16  
Old 12-24-15, 11:25 AM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
50 amp breaker. That pretty well makes it moot. You need 6-3 NM-b
Thanks Geo. With the bare ground, you couldn't use the old cable regardless. It was good for a 240V only cook top, but the range is 120/240 and requires a neutral.
Please post back when wiring the range (with the new cable) for your safety.
 
  #17  
Old 12-24-15, 12:43 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
If the circuit is EXISTING it's perfectly OK to use the SE cable for ranges,dryers,just don't remove the ground strap from the neutral connection on the appliance.
Article 250-140 NEC
 
  #18  
Old 12-24-15, 01:22 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
The bare in the SE was allowed to be used as both the neutral and ground in a 2 wire feed. The bare in NM could not be used as the neutral/ground. It was a ground only.
 
  #19  
Old 12-24-15, 02:51 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,787
Received 173 Upvotes on 156 Posts
Is this the proper cable for my new range?
What does the new range installation manual say? I'll put my money on a 40 amp circuit. The last two Whirlpool electric self cleaning ranges I have bought each specified a 40 amp circuit. The one right here in this house is a 12.6 KW range and has never tripped a 40 amp breaker. To hit the maximum rating, both broil and oven elements would have to be on in the clean cycle along with all top burners on the highest setting and then the load wouldn't be continuous as the oven elements cycle on the thermostat.

Its SE so it is a braided bare neutral.
SE cable doesn't have a braided neutral. It is bare stranded.

With the bare ground, you couldn't use the old cable regardless. It was good for a 240V only cook top, but the range is 120/240 and requires a neutral.
Like PCboss stated, SE cable was allowed to be used for a 120/240 volt feed to electric ranges and dryers. The bare neutral also carried the ground.
 
  #20  
Old 12-24-15, 04:21 PM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
If the circuit is EXISTING it's perfectly OK to use the SE cable for ranges,dryers,just don't remove the ground strap from the neutral connection on the appliance.
Article 250-140 NEC
Oops. Sorry. I was under the impression (wrong impression), a bare wire could never be used as a neutral.
 
 