Is this the proper cable for my new range?
#1
Member
Thread Starter
Join Date: Sep 2010
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Is this the proper cable for my new range?
This cable connects my electric cooktop to my electrical panel (on a 30 amp breaker). I'd like to replace the cooktop with an electric range (oven and cooktop in one.)
I have two questions:
1) What gauge is this cable?
2) What size cable and breaker do I need for the range?
Attachments:
a) picture of the cable that feeds the current cooktop
b) picture of the nameplate for the new (used) range
Any help would be appreciated.
I have two questions:
1) What gauge is this cable?
2) What size cable and breaker do I need for the range?
Attachments:
a) picture of the cable that feeds the current cooktop
b) picture of the nameplate for the new (used) range
Any help would be appreciated.
#2
Can't read the tag.... what is the wattage at 240vac ?
That is 8-2 aluminum cable. To be code compliant now it needs to be three wire with ground and for a unit your size it should be 8-3 NM W/ground.
If the range is 10.5 kw at 240v .... you're looking at a 44A load.
That is 8-2 aluminum cable. To be code compliant now it needs to be three wire with ground and for a unit your size it should be 8-3 NM W/ground.
If the range is 10.5 kw at 240v .... you're looking at a 44A load.
#9
Member
Thread Starter
Join Date: Sep 2010
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks all for your help...
Here's a better picture of the stove nameplate. Yes, 10.5 kw at 240v.
If I'm looking at a 44 amp load, then I need a 50 amp breaker, right? Will the 8 gauge cable suffice?
Here's a better picture of the stove nameplate. Yes, 10.5 kw at 240v.
If I'm looking at a 44 amp load, then I need a 50 amp breaker, right? Will the 8 gauge cable suffice?

#10
Member
Thread Starter
Join Date: Sep 2010
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I think it is copper. Two copper conductors with a braided aluminum ground (as I recall; it's been a while since I was in the junction box...)
So I know there are "preferences", but I'm trying to figure out what code requires. For this stove, would 8 gauge and 40 amp breaker be adequate? I would really, really like to not have to pull new cable, but I will if it's unsafe.
So I know there are "preferences", but I'm trying to figure out what code requires. For this stove, would 8 gauge and 40 amp breaker be adequate? I would really, really like to not have to pull new cable, but I will if it's unsafe.
#12
Member
Code is 8 gauge copper is good for 40 amps so technically you need to run a new 6/3 cable and a 50 amp breaker. Reality is that the range will work fine until you have all burners on at the same time as the oven and it pops the 40 breaker after running for an hour.
If aluminum the circuit it is only good for 30 amps and your current breaker is properly sized.
If aluminum the circuit it is only good for 30 amps and your current breaker is properly sized.
#13
I am not experienced enough to identify the cable type just by the designation, so I need help on if the cable has an insulated neutral, not a bare ground.
IF you have an insulated neutral, and it's copper cable, this installation is most likely grandfathered.
You must ensure the bonding strap was not removed though.
A typical installation would be a 40 amp breaker.
IF you have an insulated neutral, and it's copper cable, this installation is most likely grandfathered.
You must ensure the bonding strap was not removed though.
A typical installation would be a 40 amp breaker.
#14
If I'm looking at a 44 amp load, then I need a 50 amp breaker, right? Will the 8 gauge cable suffice?
#16
50 amp breaker. That pretty well makes it moot. You need 6-3 NM-b
Please post back when wiring the range (with the new cable) for your safety.
#17
If the circuit is EXISTING it's perfectly OK to use the SE cable for ranges,dryers,just don't remove the ground strap from the neutral connection on the appliance.
Article 250-140 NEC
Article 250-140 NEC
#18
The bare in the SE was allowed to be used as both the neutral and ground in a 2 wire feed. The bare in NM could not be used as the neutral/ground. It was a ground only.
#19
Is this the proper cable for my new range?
Its SE so it is a braided bare neutral.
With the bare ground, you couldn't use the old cable regardless. It was good for a 240V only cook top, but the range is 120/240 and requires a neutral.
#20
If the circuit is EXISTING it's perfectly OK to use the SE cable for ranges,dryers,just don't remove the ground strap from the neutral connection on the appliance.
Article 250-140 NEC
Article 250-140 NEC