How to get 220v to other side of house.
Received 0 Votes
I need to get 220v to the opposite side of my mobile home, the fuse box is 70 ft away from where i need it, My panel is full and I have no space to expand. My neighbor is an old electrician, 93 years old, and is a good electrician, he worked for 50 years. he says that years ago they used the carter system for getting 220v where they needed it economically.
If they had 2 separate 20 amp 120 v circuits nearby they would tap into both of them and have a 40 amp 240 volt circuit run to one device, He said this was common.
My wifes ex husband is an industrial electrician and admits that this will work but says its not a good idea. He can not explain why. I want to run romex, stapled safely under the trailer off two branch circuits to power one device.
Can i use the carter method? Or not.
You need to run one circuit of the appropriate ampacity and voltage for the load.
I am not familiar with the setup you described but it sounds like it violates the rule about paralleled cables.
If the equipment uses 240 volts but does not have subcomponents that need 120 volts then one cable of the same kind you use for 120 volts can be used for 240 volts only. If it is a 12 gauge cable then it will carry 20 amps.
For both 120 volts and 240 volts such as many electric stoves and clothes dryers need you use one 3 condeuctor (plus ground) cable.
A 12 gauge 3 conductor cable properly connected will supply two allotments of 20 amps at 120 volts or one allotment of 20 amps at 240 volts or any combination in between. Except if you draw fewer amps at 120 volts on one side you may not draw more amps on the other side to come up to 40.
Received 0 Votes
Your house is supplied with 240 volts from a transformer with a center tapped secondary, the neutral. That neutral and one of the 240 volt legs is used for 120 volts. If you connect to both 240 volts legs, each fused for 20 amps the circuit provides 20 amps not 40 amps so even if your method wasn't dangerous and non code compliant it would only supply 20 amps. Bottom line very bad idea that won't even work.
Is it really a fuse box or is it a breaker panel? Is the panel supplied by a meter and main disconnect on a pole?
It is a meter and a main disconnect on the pole,