Spa Sub Panel
Old 01-01-16, 01:13 PM
G
Spa Sub Panel
[ATTACH=CONFIG]60854[/ATTACH]
Can this 50amp Spa sub panel be used for a regular sub panel
From the looks of it The one buss bar will need to be isolated from
The box. The other one next to the lugs looks to be already grounded
The bar in the center of the box what was that used for
Old 01-01-16, 02:11 PM
G
Spa Sub Panel
Can a spa sub panel be converted as a regular sub. It's looks like it would need
One of the bus to be isolated
Old 01-01-16, 02:15 PM
Tolyn Ironhand's Avatar
Received 292 Votes on 254 Posts
Yes, however the panel should be mounted with the large hole pointing up. You will need a cover or a hub for your conduit.
Name:  sub panel.jpg
It appears that everything is ready to go as the ground and neutral bars are properly installed. White is the neutral, green is the ground, red is the hots.
Old 01-01-16, 02:31 PM
G
Thanks Tolyn, I really appreciate your help. I was looking at this and seeing neutral bus what appears to be grounded through those mounting screws going through the box after I tried following metal bar attached to it.
Old 01-01-16, 02:42 PM
ray2047's Avatar
Received 13 Votes on 11 Posts
i was looking at this and seeing neutral bus what appears to be grounded through those mounting screws
No.
Old 01-01-16, 02:58 PM
ray2047's Avatar
Gred, I have combined your multiple threads and moved them to the most relevant forum.
Old 01-01-16, 03:32 PM
G
Thanks Ray, I appreciate it
Old 01-01-16, 07:28 PM
G
I have another question what if Once I put the 60 amp breaker in my main panel replacing 2- 15 amp breakers and those wires are too short to get to the sub what's the best way to extend those wires
Old 01-01-16, 09:01 PM
ray2047's Avatar
What two wires? Do you mean the two hots in the supplying panel? If so just use wire nuts to extend them.
Old 01-02-16, 10:38 AM
CasualJoe's Avatar
Received 99 Votes on 89 Posts
That bar in the center is used to bond the neutral bus to the panel box in some applications. As pictured, the neutral bus is isolated from the box.
Looks like a GE panel.
Old 01-02-16, 10:47 AM
G
Thanks Ray, I would have to remove 2 15 amp circuits, to plug in my 60 amp breaker. So those two circuits would have to go over into the sub. now here is my other dilemma, these circuits are aluminum, can I just get those aluminum wire nuts and apply some anti-oxidant to extend those branch wires?(copper pigtailing) I realized when I had an electrician install my hot tub few years back, he hard wired that into my panel,..and now seeing inside of it. Im not sure if it was him or it was already there but I have a double tap on my main for a circuit. I found this out when I was trying to label all my circuits. so that's another cuircit that would have to moved over. this would leave me with one open slot in my sub. 2 circuits gets moved replacing the 60 amp for sub.. and that 3rd for that one circuit that's double tapped.
another thing is.. this sub, is I believe rated for 125amps would this be correct?? is states "max branch or main circuit breaker rating 125 amps"
[ATTACH=CONFIG]60927[/ATTACH]
Old 01-02-16, 11:01 AM
CasualJoe's Avatar
The Ideal purple #65 Twister wire nuts are great for aluminum to copper if this is just a temporary connection. For a permanent connection you need to do it right and use AlumiConn connectors. The Ideal purple wire nuts have an unusually high failure rate.
Shop Alumiconn 10-Pack Plastic Standard Wire Connectors at Lowes.com
Old 01-02-16, 11:05 AM
G
Yea I forgot about those AlumiConn connectors .. I actually have them saved in my list on ebay. So I will do it that way. thanks for reminding me..
would 6-3 wire be ok for this
Old 01-02-16, 11:12 AM
CasualJoe's Avatar
6-3 NM-B cable (aka romex) is fine to feed the subpanel.