Old 01-02-16, 10:35 AM
Member
Thread Starter
Join Date: May 2009
Location: central
Posts: 25
Smile small heater

I have a small elect heater for a family room downstairs. Have 3 outlets on a 20amp bk. The outlet that I'm going to use is at the end of the line. Can I use the outlet that is there or do I need to install a GFI. Have outside wall in room insulated and have a heat run for room, just doesn't seem enough.
 
Sponsored Links
  #2  
Old 01-02-16, 10:58 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,285
No GFCI is required in a finished basement family room.
 
  #3  
Old 01-02-16, 10:58 AM
Member
Join Date: Sep 2009
Location: Louisville KY
Posts: 571
There is no need to install a GFCI receptacle just because you're plugging a heater into it. The need for a GFCI receptacle is determined by the location of the receptacle, not what is plugged into it.
 
  #4  
Old 01-02-16, 11:04 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,058
No such thing as a small electric 120 volt heater. They almost all are 1500 watts unless they have a switch for choosing the watts. It would be best to not have anything else plugged into the circuit or use it on less than 1500 watts. (1500 watts = 12.5 amps.)
 