Running new circuit question

Never ran a new circuit but for curiosity for the future....

I thought code required the wire be secured to say a 2x4 within 8" (?) of the outlet via staples.

How does one do that when pulling the wire behind drywall down to a lower location?
 
Sponsored Links
  #2  
Old 01-12-16, 11:53 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,385
How does one do that when pulling the wire behind drywall down to a lower location?
When fished the cable doesn't need to be secured to the stud.
 
  #3  
Old 01-12-16, 08:31 PM
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 4,251
Old work boxes (the kind you would mount in a hole in the drywall) have a clamp on them that hold the wire securely and remove the requirement for fastening with a staple.

Most (some) new work boxes don't have that same clamp, and require fastening within 8".
 