GFCI Trip
Probably a basic question but I'm kind of stumped. Have electrical run to the shed and found the gfci tripped tonight. I'll try to keep this as short as possible.
I have 12/2 uf running from breaker panel in house and out to the shed. It runs to an exterior mounted waterproof in-use box with the gfci and then into the shed. Only thing plugged into the shed was a radio. Current temps have been in the 20s and 30s. Would this be an issue inside of the shed or could there be an issue in the line under ground. I'm assuming that if it was in the ground, the breaker would have tripped.
I have 12/2 uf running from breaker panel in house and out to the shed. It runs to an exterior mounted waterproof in-use box with the gfci and then into the shed. Only thing plugged into the shed was a radio. Current temps have been in the 20s and 30s. Would this be an issue inside of the shed or could there be an issue in the line under ground. I'm assuming that if it was in the ground, the breaker would have tripped.
#2
Welcome to the forums. It really indicates that you have a "ground fault" somewhere. Water/moisture can have an effect on the external receptacle and can trip it, however. You could have a nick on the UF cable causing it to fault. Remember a GFCI does not trip with overload, but with a differential between the hot and neutral. Double check your connections in the receptacle box and at the receptacle box in the garage.
#4
If it's the GFI receptacle on the shed that is tripping then it's not a problem with the wiring from the house to that point. The GFI can only protect itself and whatever is attached to the load terminals.
It is very likely the GFI receptacle has moisture in it causing it to trip. It would be better if you could put the receptacle inside the shed and feed the outside receptacle as a load.
It is very likely the GFI receptacle has moisture in it causing it to trip. It would be better if you could put the receptacle inside the shed and feed the outside receptacle as a load.