Changing Cu to PEX - what about ground?

if I want to completely change copper pipes to PEX...what do I do with the existing grounding wires ? I see jumpers on my water heater and later by the water meter.... Do I just disconnect them all and leave only the main ground which goes from the main panel directly to the water pipe BEFORE the water meter....so this is fact would still be the only copper pipe going into the Ground.

Thanks!
 
Sponsored Links
  #2  
Old 01-20-16, 08:15 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,051
Received 26 Votes on 20 Posts
You won't need the jumpers at the water heater. Assuming you are not changing the water service into your house to plastic, you still will need to have a GEC to within 5 feet of where the water service enters the house and jumper around the meter in one continuos length. Use #4 copper or #2 aluminum for a 200 amp service OR #6 copper or #4 aluminum for a 100 amp service.
 
  #3  
Old 01-20-16, 09:24 PM
Member
Join Date: Sep 2009
Location: Louisville KY
Posts: 578
Received 0 Votes on 0 Posts
What's the purpose of jumping around the meter if all of the pipe on the homeowners side is PEX?
 
  #4  
Old 01-20-16, 10:33 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,945
Received 31 Votes on 27 Posts
The jumper was in place when the house was plumbed with copper. The copper is being replaced with pex.
 
  #5  
Old 01-21-16, 10:48 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,051
Received 26 Votes on 20 Posts
Yes, if everything after the meter is pex there is no jumper around the meter required.
 
  #6  
Old 01-21-16, 03:43 PM
Member
Thread Starter
Join Date: Jan 2015
Location: United States
Posts: 460
Received 2 Votes on 2 Posts
ok...so I am just removing all grounding up to the meter.

and sicne I am running 200Amp service I just run a new #4 green wire from the main panel to the point before the meter.

thanks!
 
  #7  
Old 01-21-16, 08:08 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,051
Received 26 Votes on 20 Posts
#4 bare copper is what is normally used, either solid or stranded, but green insulated copper is acceptable too. If cost is an issue, use #2 aluminum.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: