Not getting 240v to 240v appliances.

attached is a pic of my home circuit breaker box. all the circuit breakers check out good. the one's marked i'm not getting 120 v. and 220 appliances are only getting 120 v. any idea how to fix? thanks in advance.
 
Attached Images  
  #2  
Old 01-26-16, 10:05 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Call the electric company and tell them you have a bad leg.
 
  #3  
Old 01-26-16, 10:05 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
Call your power company first. All those breakers are on the same leg of the panel.
 
  #4  
Old 01-26-16, 10:06 AM
M
Member
Thread Starter
Join Date: Jan 2016
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
i called the electric company and i'm getting 240 v to circuit box and master switch. i meant to when i use a mulitmeter on the master switch i'm getting 240 v but to the range, ac, and central air only 120 on one side and 0 on the other like in the pic
 
  #5  
Old 01-26-16, 10:11 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,017
Received 3,406 Upvotes on 3,056 Posts
Did you take the cover off the panel in the picture and check for 240v there ?
 
  #6  
Old 01-26-16, 10:15 AM
M
Member
Thread Starter
Join Date: Jan 2016
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
yes, took panel off and checked every circuit breaker. those with the x are 0 v and anything not checked is 120 v. all the circuit breakers are good. i pulled each one and tested it for resistance in the "on" position.
 
  #7  
Old 01-26-16, 10:21 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,017
Received 3,406 Upvotes on 3,056 Posts
If you have 240v on the wiring to the main breaker but not after..... it looks like the main breaker is defective. Have you tried turning it off and back on ?

It may be a corroded bus bar where the main breaker attaches. You need to be very careful as you cannot remove that breaker live.
 
  #8  
Old 01-26-16, 10:27 AM
M
Member
Thread Starter
Join Date: Jan 2016
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
yes, i've tried turning the main breaker on and off. but i'm getting 240 volts on the main breaker from both 120 volt switches. i don't know how to safely pull the main breaker because it has a screw holding it in and it will be live. and yeah it could be a corroded busbar going to the other 240 volt circuit breakers. hmmmm what to do. i'll have to look and see if i can turn it off outside the breaker box.

oh well, i got a electrician coming in a couple of hours and it should cost about $100. $30 for service call and $70 an hour. thanks for the help. i'll let you know how it goes.
 
  #9  
Old 01-26-16, 12:41 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
I know you have an electrician coming but just for info I think you are a bit confused about breaker boxes. You wrote:
but i'm getting 240 volts on the main breaker from both 120 volt switches.
There are no 120 volt switches. There are in fact no switches per se in a breaker box. There is a 240 volt main breaker and mesuring between the two legs you should read ~ 240 volts.
 
  #10  
Old 01-26-16, 02:37 PM
M
Member
Thread Starter
Join Date: Jan 2016
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
well it turns out one side of the main breaker was bad. i couldn't tell because the wires coming from the meter will always read 240 v. all the electrician did was remove the meter which made it not live and replaced the main breaker switch. the problem was he left for over an hour and the call was only $30 and $70 dollars an hour for labor. i got charged $234. the place was in Shepherdsville, KY. he was barely here an hour and even if he went over an hour it would have been 170 plus $10 for the switch which would have been $180. i can't help but feel i got burned. i think they have a minimum of 2 hours which they don't tell you and there is some unknown charges. i'll have to review the invoice.

i came close to being able to fix it but at least i learned something new.
 

Last edited by Tolyn Ironhand; 01-27-16 at 05:51 PM. Reason: Removed name
  #11  
Old 01-26-16, 03:24 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
I doubt he had a main breaker on his truck so he had to drive to a supply house to buy one.
$10 for the switch
To repeat it was a breaker not a switch. Two very different things. Breakers are specific to the panel but even if it was a Square-D and only 100 amps some versions would have been $100 or more.
i got charged $234
$234-$30-$70=$134 dollars for a breaker. Not an unreasonable price especially adding in his cost to go get the breaker.

Tell us the amps of the main breaker and the make and model number of the panel or the listed types of main breaker on the label inside the panel and we can help more with price. (Or wait to see if a pro can identify from the picture.)
 
  #12  
Old 01-26-16, 04:14 PM
M
Member
Thread Starter
Join Date: Jan 2016
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Eaton Type Ch 100 Amp Double-Pole Circuit Breaker
$68.48

i'm sure they had this at lowes. if i wasn't so ignorant i would have bought the part and had it there when he arrived.

well i was charged $54 for the main breaker but $150 for 2 hours and $30 call so 70 + 70 + 10? +54 + 30 = 234. the problem was it should have only taken 10 minutes to replace the part. i mean if i was sure that part was bad i could have went and got it and even if it wasn't the right one i could take it back and get a refund. i just feel they have a 2 hour minimum on a service call which they don't tell you.

oh well it was a lesson learned. if i have any more problems like that, they will be a lot easier to solve since i did spend some time trying to solve this problem and also help here on this forum.

Name:  main.jpg
Views: 2324
Size:  17.3 KB
this is a replacement for the brand i had "Challenger" which was bought out by Eaton. on the home depot website you can find a list that shows the replacement if your brand went out of business or bought out.
 
  #13  
Old 01-26-16, 05:46 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
I wo say you got quite a deal. I doubt they made any money on that job.
 
  #14  
Old 01-26-16, 06:33 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
Eaton Type Ch 100 Amp Double-Pole Circuit Breaker
$68.48

i'm sure they had this at lowes. if i wasn't so ignorant i would have bought the part and had it there when he arrived.
It wouldn't have helped one bit had you bought the circuit breaker ahead of time, that is the wrong breaker. What replaces Challenger breakers and what fits your panel is Eaton/Cutler-Hammer BR series breakers. That screw you mentioned is the main breaker hold down kit, I hope the electrician replaced it, it is required. The CH series and BR series breakers are not interchangeable.
 
  #15  
Old 01-27-16, 02:22 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Sounds like a very fair price on a main breaker replacement. You got lucky on Eaton BR being a relatively cheap, in-stock item. Some panels the breaker alone is $300 special order. There would have been no realistic way to know in advance if the problem was the breaker, the panel or both. The electrician had to disconnect the meter and inspect the breaker and panel to know which parts to buy.
 
  #16  
Old 01-27-16, 03:04 PM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
i got charged $234
I wouldn't say you got burned or even overcharged. $70 an hour is low for an electrician, especially dealing with pulling a meter.
 
 