Romex in Attic


  #1  
Old 01-28-16, 07:06 AM
D
Member
Thread Starter
Join Date: Jan 2016
Location: USA
Posts: 43
Upvotes: 0
Received 0 Upvotes on 0 Posts
Romex in Attic

Hey guys -

Need to run some new Romex in my unfinished attic. There are no stairs or ladder at the entry hole, as is completely what you'd consider an "unusable attic space."

My question is can I run Romex perpendicular across the ceiling joists (stapling at each one)? I'd rather not drill holes if I don't have to considering it's not close to the entry hole (more than 6 feet away).

Thoughts?
 
  #2  
Old 01-28-16, 07:08 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
Yes, and you only need to secure at intervals of no more than 4 1/2', every truss is not needed.
 
  #3  
Old 01-28-16, 07:08 AM
P
Temporarily Suspended
Join Date: Jul 2008
Location: NY
Posts: 10,265
Upvotes: 0
Received 0 Upvotes on 0 Posts
Staples are fine for Romex. You probably won't have to staple it to every joist.
 
  #4  
Old 01-28-16, 07:20 AM
D
Member
Thread Starter
Join Date: Jan 2016
Location: USA
Posts: 43
Upvotes: 0
Received 0 Upvotes on 0 Posts
Does the ability to run it over joists (without drilling) end if I get within 6 feet of the entry hole? Or at what point will leaving the wire that exposed not suffice?
 
  #5  
Old 01-28-16, 07:27 AM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
You don't have to drill holes no matter where the cable is running. Drilling through rafters and joists is for when that's the only way.

I would say the cable also doesn't need stapled, if you consider this "inaccessible" or you are going to great lengths just to get a few staples in.
 
  #6  
Old 01-28-16, 07:30 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
If you can walk through, or there is designated storage in the attic, the cable needs to be protected with substantial framing (2x4). If it is a generally inaccessible attic, the cable needs protection only within 6' of the scuttle hole.
 
  #7  
Old 01-28-16, 07:31 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
It only needs to be protected within 7' of the access hole. Add a running board next to the cable to prevent damage.

Trusses do not get drilled.
 
  #8  
Old 01-28-16, 01:49 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
If it is a generally inaccessible attic, the cable needs protection only within 6' of the scuttle hole.
I once heard an inspector say, "if it has a scuttle hole, it is accessible." I think accessible is up to the AHJ.
 
  #9  
Old 01-28-16, 03:20 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
Here is the NEC:

320.23 In Accessible Attics. Type AC cables in accessible attics or roof spaces shall be installed as specified in 320.23(A) and (B).
(A) Cables Run Across the Top of Floor Joists. Where
run across the top of floor joists, or within 2.1 m (7 ft) of
the floor or floor joists across the face of rafters or studding,
the cable shall be protected by substantial guard strips that
are at least as high as the cable. Where this space is not
accessible by permanent stairs or ladders, protection shall
only be required within 1.8 m (6 ft) of the nearest edge of
the scuttle hole or attic entrance.
(B) Cable Installed Parallel to Framing Members.
Where the cable is installed parallel to the sides of rafters, studs, or ceiling or floor joists, neither guard strips nor running boards shall be required, and the installation shall also comply with 300.4(D).

This section also applies to Article 334, NM cables.
 
 