Basic Grounding question

Can all the grounding wires be connected to the grounding screw on the device ?
(either a switch or receptacle or even porcelain light fixture)

Rather then create a pigtail which in effect requires four wires(one wire to device, one to metal box, one incoming from cable feeding box and one outgoing from cable leaving box) is it acceptable to connect all the ground wires directly to the green screw on the device allowing there to be one less grounding wire?
 
Sponsored Links
  #2  
Old 01-31-16, 08:44 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
No. One wire per screw. Box fill counts the total grounds as "1" not each so nothing would be gained.
 
  #3  
Old 01-31-16, 08:50 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,975
Received 35 Votes on 30 Posts
The wires would be very hard to secure properly under one screw head. Follow the advice above.
 
  #4  
Old 02-01-16, 06:09 PM
Member
Thread Starter
Join Date: Nov 2001
Location: usa
Posts: 417
Received 1 Vote on 1 Post
The only issue I find is it requires adding an extra wire to each box which can make things fairly crowded in the box. It seems neater and more roomier doing it the other way. Putting code aside for the moment - electrically what is the a? Are you not accomplishing the exact same thing?


Must each individual metal box along the circuit be grounded? It seems like not infrequently when I open up a box in my "older" house - whether to change a switch or receptacle very often there is no separate ground wire going to a screw on the box. Often the grounds from the incoming and outgoing cables are wrapped around the grounding screw on the device or if there is no outgoing cable the ground is just attached to the grounding screw on the device. Does this pose a danger? If it is a receptacle in the box and I use a tester it will read that it is grounded despite there being no ground to the box.
 
  #5  
Old 02-01-16, 08:47 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,975
Received 35 Votes on 30 Posts
Grounding requirements have changed over the years.

Trying to stack 4 wires under a screw head will not give a reliable connection.
 
  #6  
Old 02-02-16, 08:01 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Code requires an unbroken mechanical connection (wirenut, screw terminal, crimp) on ground wires, and ground integrity cannot depend on the device. In other words if you remove the receptacle, the rest of the circuit must still be grounded. In fact grounds must be fully made-up and continuous prior to rough inspection when power isn't even turned on yet. If the grounds were spliced on the device screw, this requirement would be violated.

If you really want to save box space you can use a barrel crimp and leave one of the ground wires long to wrap the device screw. That takes almost no space, but is harder to rework in the future if necessary.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: