Wiring colors on 240v breaker
Old 02-13-16, 02:52 PM
G
Is there any circumstance that it matters what breaker terminal you connect the red and black wire? Working on a new 50 amp range receptacle and breaker.
Old 02-13-16, 02:59 PM
L
Received 105 Votes on 91 Posts
It does not matter.
Only case it matters I can think of is when there are 2 breakers feeding same device.
Old 02-13-16, 03:05 PM
ray2047's Avatar
Received 13 Votes on 11 Posts
Assuming single phase it doesn't even have to be black and red. It could be black and black or black and a white* that has been recolored red or black or any color but (white), gray or green.
*A black and recolored white are acceptable for cable but white should not be used in a conduit system. Canadian code may vary.
Old 02-13-16, 05:52 PM
A
Received 134 Votes on 123 Posts
The range probably uses both 120 volts and 240 volts and if so it requires a neutral. So you run cable or conduit with 3 conductors plus ground. The white is the neutral of course.
If separate breakers are used for the two hot legs the breakers must be next to each other hand have their handles tied together.
Old 02-13-16, 07:14 PM
ray2047's Avatar