Surge still blows furnace control board out
#41
And so surges blew the old one, and surges blew the new one.........
#42
Hi Geo.....Always had the Genny from since shortly after the house build.
And Westom...you're still analyzing, but not applying analysis or recognition to your own inability to relate properly. And that is FAR more important than anything you could ever know or prove about anything.
Here's a tip...when you admit to being off base or relating poorly...historically people actually wind up liking you better.
#43
Joe, I agree. The line power should be stable by the time the transfer switch decides to cut over. I'm just not familiar with how they accomplish that transfer, relay or some softer approach like syncing the gen to the line first. Doubt if they sync the two.
If it is just a relay and it is generating some sort of spike, wouldn't there be a protection circuit on the output of the generator, in this case that is no longer working?
Bud
Bud
#44
Since you listened to Furd, then what he suggests may be impossible.
Furd only understands throwing darts.
While I agree completely in determining the CAUSE of the problem rather than just making non-logical attempts to circumvent the problem, I have yet to see westom give a detailed list of troubleshooting steps, in any of his responses.
It already exists inside every furnace controller and all other appliances. Described is a transient that exceeds what appliances are already designed to withstand without damage. Existing internal protection is robust.
#45
I'd look a little harder at the transfer switch or possibly the generator.
Is this a 120V furnace; at least at the fan/controller board input?
The problem I have in designing experiments for the owner is that without test equipment, about the only indication of a problem may be more blown boards. Not many of us have differential dual channel, high voltage storage oscilloscopes.
In spite of that, what could be done is use test lamps on each leg of the line. Someone had suggested this before. Furnace OFF, along with any electronics and appliances, stereos, TV all unplugged. Go thru some test cycles on the genset and transfer switch. The transfer switch will have a UTILITY IN breaker. Use that to test the system manually. This is not the PANEL MAIN breaker. Make sure the test lamps switch cleanly, especially with NO BRIGHT pulses. Use some unsophisticated loads, like a couple of space heaters, one on each line.
good luck in the hunt.
ps; I'd use incandescent lamps, and the other transient to look for is a clean turn on to utility power. If the transfer relay is arcing more than usual at the reconnect, you will get very rapid voltage transients during the arc. This can be hazardous to electronics. Called EFT or electrical fast transient in the industry.
Last edited by telecom guy; 02-29-16 at 07:14 AM. Reason: clarification, spelling,
#47
All of the residential grade transfer switches are ultimately just a double pole relay. They do not sync or co-switch. The two poles are supposed to break-before-make and should be "simultaneous" within the tolerance of a magnetic relay. Most of them have a fixed delay in seconds (usually 10s) between line power restoration (which is measured by RMS voltage +/- 10% of nominal; no fancy waveform analysis) and the transfer action.
A few things are still bounding around my head -- is the relay in the transfer switch really working correctly? Is it chattering, are the contacts arced, are the poles acting independently (perhaps bent/broken internal component)?
If OP is in the country and all or most of his neighors also have transfer switches and automatic generators, then maybe there are big power anomalies happening as all of the neighboring houses cut back on to the utility. The effect would be particularly pronounced if he shares a transformer on the end of a long line.
In any case, this is going to be pretty tough to do any real diagnostics on without quality metering equipment. A standard multimeter is not going to catch anything meaningful in that short of a timespan. Once you've done the basic mechanical inspections of everything, verified good grounding, verified correct wiring, I think the next step is to have the generator and switch inspected by a factory certified tech who can scope it and verify proper electrical operation.
#48
Hi Ben, Yes this is what I'm doing, my "next step is to have the generator and switch inspected by a factory certified tech who can scope it and verify proper electrical operation."
And thanks Geo but I've run out of bandwidth to deal with this any further...aside from checking if there's actually ground rods outside, then checking for a short between gnd and neutral between furnace and panel....which I know means disconnecting both ends or looking physically.
Also FYI Westom has been banned from the forum.
#49
Well yes, what we found is that the genny, as measured at its panel, was putting out 160 volts between each leg/phase and neutral instead of the the usual 120v.
So the 160v bypassed the gen panel surge protector and bypassed the dedicated surge protector at the furnace and fried a bunch of stuff in the furnace!!
We have since had the genny output voltage corrected.
It could also be partly a POCO issue too. (power co)
Measure what's coming out of the genny panel, and get sp's installed too. But remember sp's only work well if you have proper grounding, which the other pros will better comment on.
#52
The generator was putting out 160vac...... that would be 320vac across the hot legs.
What make was this generator ?
I've installed a lot of them and have never seen that problem. The generator's electronics should have shut that generator down.
Technically, if the 160vac was the problem the furnace board should have fried as soon as it went to generator power. 160v is not a surge..... it is an over voltage problem. A surge protector protects against an instantaneous large spike.
The part that is baffling is why at the transfer point. I'm thinking that maybe the furnace blower was running at the time and the removal of power caused it to spike. Everything was running hot at 160v.
It's hard to believe only the furnace was affected.
#53
It looks a little confusing. A new member posted here about his problem. In order to not get the two issues confused.... I moved the new member to his own thread which can be found here... http://www.doityourself.com/forum/el...ace-board.html
Sorry for any confusion.
#54
Generac genny. And we measured continuous 160v at the genny sub panel and at the input to the furnace. This was while the poco power was out and we're only on genny power.
No other things were affected. This condition also fried 2 other SPD outlet strips in the house. But thank fully saved the devices, computer and entertainment center stuff, on the strips. Didn't check voltage at these places though.