What size circuit breaker for residential water heater?

40 gallon electric water heater. Dual 4500 watts. What's the correct size wire and circuit breaker?
 
  #2  
Old 02-25-16, 10:29 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
#10-2/g cable and 30A double pole breaker. Some jurisdictions require a disconnect at the unit (air conditioner pull-out style is OK). Some jurisdictions require that the connection from the wall/ceiling to the unit be protected -- flex conduit or metal cable for example.
 
 