NEMA 14-30P Dryer Receptacle
#1
Member
Thread Starter
Join Date: Jun 2009
Location: PE, Canada
Posts: 102
Upvotes: 0
Received 0 Upvotes
on
0 Posts
NEMA 14-30P Dryer Receptacle
I'm replacing a 20+ year old dryer. The receptacle appears to be a NEMA 14-30P with two 30 Amp breakers. Do receptacles change? Has the NEMA 14-30P remained the same for longer than 20 years? It seems reasonable to assume a standard is a standard but the cost of that assumption would be very high if incorrect. Can I safely plug a new dyer into the receptacle?
#2
Member
The NEMA 14 30P and matching receptacle 30R are the present ones to use with the dryer. It is a 3 pole 4 wire set up.
You can go here and see if the plug/receptacle match what you have. Keep in mind the configuration is different for all 120 240 and amp rated plug/receptacles for the reason that they can not be used incorrectly. Does not mean that the wires being used are correct but only that the plug will only match the receptacle.
I do not know what the codes are in Canada though.
You can go here and see if the plug/receptacle match what you have. Keep in mind the configuration is different for all 120 240 and amp rated plug/receptacles for the reason that they can not be used incorrectly. Does not mean that the wires being used are correct but only that the plug will only match the receptacle.
I do not know what the codes are in Canada though.
#4
Member
Thread Starter
Join Date: Jun 2009
Location: PE, Canada
Posts: 102
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks AFJES for the plug/receptacle chart.
pattenp:
Can one 30A double pole breaker be two singles fastened together on the switch toggles? That is what is in place presently.
pattenp:
Can one 30A double pole breaker be two singles fastened together on the switch toggles? That is what is in place presently.
#5
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,665
Received 254 Upvotes
on
217 Posts
Can one 30A double pole breaker be two singles fastened together on the switch toggles? That is what is in place presently.
#6
Member
Thread Starter
Join Date: Jun 2009
Location: PE, Canada
Posts: 102
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I am completely uncertain. It ran a Kenmore dryer previously and has a 30R receptacle as described in the link provided by AFJES. I will see if I can find the specs on the Kenmore.
Thanks
Thanks
#7
The brand of the dryer doesn't matter. When you connect the dryer to the house you put on the correct cord to match the receptacle you have available. The old style dryer plug is 11-30R and the new style is 14-30R. The code changed around the mid-1990s If you have an 11-30R in your house you may continue to use it, but if you add a new dryer circuit or move the existing one it must be upgraded to the new standard 14-30R.
When you hook up your new dryer, buy the cord (or take the cord off the old one) and put it on the new dryer. The manufacturer should provide instructions for connecting a 3 wire or a 4 wire cord. It will require you to either disconnect or connect a neutral bonding strap inside the dryer's wiring compartment.
When you hook up your new dryer, buy the cord (or take the cord off the old one) and put it on the new dryer. The manufacturer should provide instructions for connecting a 3 wire or a 4 wire cord. It will require you to either disconnect or connect a neutral bonding strap inside the dryer's wiring compartment.
#8
Member
Thread Starter
Join Date: Jun 2009
Location: PE, Canada
Posts: 102
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks ibpooks. The dryer was purchased in 1992 (I think) and according to the chart is a 14-30R and not a 11-30R, as those seem to be the only likely options, all seems good to go.
#9
according to the chart is a 14-30R and not a 11-30R,