need some help with a 100 amp sub panel
#1
Member
Thread Starter
Join Date: Feb 2014
Location: usa
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
need some help with a 100 amp sub panel
I want to install a sub panel to my shop, the sub panel will be about 200 feet away from the main panel the main panel is a 200 amp service, would a 100 amp service be enough I will have a welder running off if it that draws less than 30 amps ad 240v I have a compressor running off of it not sure of the amps over head lights and probly about 5 110v outlets in the shop. What size and type of wire wpuld I need to go from the sub panel to the main panel and if ypu could think of anything else that I would need Thanks
#2
You can run a whole house on 100 amps so a shop should be fine. Your receptacles will be 120 not 110. If this is detached you will need to run conduit with four individual wires buried 18" or cable direct buried at 24". Best practice is to not run cable in conduit.
If detached shop at the shop you will need a 100 amp main breaker panel and a ground rod. Most panels do not come with a ground bar so you will need to buy and add a ground bar. The panel neutral bar will not be bonded to the panel so the bonding strap or screw will not be used.
At the main panel you will install a 100 amp breaker. Wire size depends on type used and whether copper or aluminum but it will be #2 or larger except for the ground wire.
If detached shop at the shop you will need a 100 amp main breaker panel and a ground rod. Most panels do not come with a ground bar so you will need to buy and add a ground bar. The panel neutral bar will not be bonded to the panel so the bonding strap or screw will not be used.
At the main panel you will install a 100 amp breaker. Wire size depends on type used and whether copper or aluminum but it will be #2 or larger except for the ground wire.
#3
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,619
Received 240 Upvotes
on
204 Posts
For a 100A feed to your shop I highly recommend 2/0-2/0-2/0-1 aluminum Mobile Home Feeder (MHF). I also highly recommend you use PVC conduit where buried even though MHF is direct bury rated. It does have to be in conduit where inside the structure. 200ft is a long run and this size feeder is needed to prevent any possible large voltage drop. You could go with 2-2-2-4 MHF but the max you should go is about 70A at that distance.
#4
Note mobile home feeder can not be run into buildings unless it is dual rated. Basically that means if the individual wires are not marked as a type of wire that can be used in building it can't enter a building.
#5
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,619
Received 240 Upvotes
on
204 Posts
Mobile Home Feeder is rated as RHH/RHW-2/USE_2 and can be installed inside the structure, but does need to be in conduit. Do not confuse MHF with URD. URD is just USE-2 and is not rated for inside and must be terminated outside of the structure.
#8
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,619
Received 240 Upvotes
on
204 Posts
No. Example is if a main lug panel is used as a subpanel and you install a back fed breaker to be used as a main breaker then that breaker needs a retainer clip. The breaker back in the primary panel feeding the subpanel is not considered as being a main breaker and does not need a retainer clip.
#11
Member
Thread Starter
Join Date: Feb 2014
Location: usa
Posts: 9
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the info the panel I have is a square d home line 125 amp panel with 100 amp breaker is that good or should I get something else also I'm still a little confused on how I make my connection at the main panel in the house
#12
I have is a square d home line 125 amp panel with 100 amp breaker is that good
I'm still a little confused on how I make my connection at the main panel in the house
#13
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,619
Received 240 Upvotes
on
204 Posts
the panel I have is a square d home line 125 amp panel with 100 amp breaker
I'm still a little confused on how I make my connection at the main panel in the house