Will this be to code...pass inspection
#1
Member
Thread Starter
Join Date: Sep 2006
Location: Minnesota
Posts: 72
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Will this be to code...pass inspection
Hello. Please refer to the attached image. I needed a bottom mount box so I pieced PVC and metal together to get the volume I needed. Is there anything wrong with this? Is my use of the metal retainers on the sides OK? I will be getting this inspected and my state and town follow the 2014 national codes. Note I will be putting a second switch on the left side of the box. This is work in progress and I figured I'd check on the legality of this before finishing up
Thanks
Thanks

#2
Use a plastic ring or switch to a metal box.
Also the cable connector should be outside the box, not inside like on the left.
Also the cable connector should be outside the box, not inside like on the left.
#3
Looks like you are really hurting for space in that box. That connector on the left will be a problem even when it's installed correctly.
#4
Member
Thread Starter
Join Date: Sep 2006
Location: Minnesota
Posts: 72
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks. I'll get the plastic rings. As for hurting for space, the box plus the metal front is 32 cu in. And I have 2 switches and 10 wires, all 14 gauge. So unless my calculations are wrong, that takes up all 32 cu in. Did I miss something?
#6
Member
Thread Starter
Join Date: Sep 2006
Location: Minnesota
Posts: 72
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'm not sure I understand your math. My understanding of the code is as follows:
10 wires at 14 gauge: 2*10=20 cu in
2 switches: 4*2=8 cu in
All ground wires: 2 cu in
All internal cable clamps (I.e. wire nuts): 2 cu in
Total: 32 cu in
You calculated 30. What did I miss?
10 wires at 14 gauge: 2*10=20 cu in
2 switches: 4*2=8 cu in
All ground wires: 2 cu in
All internal cable clamps (I.e. wire nuts): 2 cu in
Total: 32 cu in
You calculated 30. What did I miss?
#7
Member
Box Volume
All internal cable clamps (I.e. wire nuts): 2 cu in
#8
Wire nuts are not clamps, nor do they count towards box fill under the NEC. Clamps hold cables in the box.
#9
Member
Thread Starter
Join Date: Sep 2006
Location: Minnesota
Posts: 72
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks...I assumed the clamps were the wire nuts and added 2 or 2.25 (depending on wire gauge) to every box to account for this. So I can subtract that number from all my future boxes.
I plan to remove those metal clamps and replace with the plastic ones. Or, could I just convert to a metal box? I assume there is no code issue with using a metal box in place of the PVC one in the picture. And I will reverse the clamps so the screws are on the outside.
Thanks!
I plan to remove those metal clamps and replace with the plastic ones. Or, could I just convert to a metal box? I assume there is no code issue with using a metal box in place of the PVC one in the picture. And I will reverse the clamps so the screws are on the outside.
Thanks!
#10
The box and the extension ring can either both be plastic or both be metal, not mismatched. If you use a metal box, you'll need to bond your ground wires to the box via a green ground screw.
#12
There are two cables from the right and one from the left.
You can see there are two white and two black wires in the box before the third cable is stripped.
You can see there are two white and two black wires in the box before the third cable is stripped.