Smoke Alarm hard wiring problem

I am putting in two new hard wired smoke alarms with battery backup and when I try and connect them to the wiring, they activate and will not stop. So after scratching my head and poking around, I've found that the voltage reading between hot and neutral is just 20 volts. The voltage between neutral and ground is 120 and between hot and ground it is 98 volts. It's the same on both alarms which are on the same circuit.

So I'm thinking this means I have an open connection in the circuit somewhere. But do these readings mean I have an open in the hot or neutral or ground? And what's the best way to track it down? The home is super old and I'd like to try and figure out a faster way of tracing the circuit rather than open dozens of outlets and light fixtures to try and spot a loose connection somewhere.

Any suggestions?
 
Sponsored Links
  #2  
Old 05-02-16, 01:49 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,983
Received 35 Votes on 30 Posts
What is the wiring method used?
 
  #3  
Old 05-02-16, 02:20 PM
Member
Thread Starter
Join Date: May 2016
Posts: 5
Received 0 Votes on 0 Posts
Not sure I understand the question, but the 120v harwired smoke alarm has a connector with 3 prongs- hot, neutral and interconnect(black , white, red). Typical residential alarm
 

Last edited by pcboss; 05-02-16 at 03:27 PM. Reason: interconnect was ground.
  #4  
Old 05-02-16, 03:11 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
How about the wiring in the walls? How many alarms are there? Are they all interconnected? Are the units compatible per manufacturer specs (not all of them can interconnect)?
 
  #5  
Old 05-02-16, 03:51 PM
Member
Thread Starter
Join Date: May 2016
Posts: 5
Received 0 Votes on 0 Posts
The wiring is the box for the alarms have red, black and white as well.

I know that the two that I'm trying to replace are on the same circuit but not sure if there are other alarms or lights or anything else on the circuit or not. It's a large old place so I haven't been able to track it all down easily.
 
  #6  
Old 05-02-16, 04:38 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Normally power goes to black and white and remote alarm connection to red. Is that what you have.
 
  #7  
Old 05-02-16, 05:27 PM
Member
Thread Starter
Join Date: May 2016
Posts: 5
Received 0 Votes on 0 Posts
Yes, I just read the instructions and agree that black is meant for hot, white is neutral and red is to interconnect. (Not what I previously had posted)

I think that may have solved the issue. I assumed the wires were hot, neutral and ground, but I was wrong. The interconnected wire may be interfering with another fixture. I'll try to adjust and be back with an update
 
  #8  
Old 05-02-16, 05:57 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
The interconnected wire may be interfering with another fixture
Different makes and models often don't play well together.

Tip: If it isn't green or bare it isn't ground.
 
  #9  
Old 05-03-16, 09:35 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Yes you found it -- red is interconnect. The plastic residential smoke detectors are not grounded. You splice the ground wires in the box, but they do not connect to the smoke detector.
 
  #10  
Old 05-03-16, 02:35 PM
Member
Thread Starter
Join Date: May 2016
Posts: 5
Received 0 Votes on 0 Posts
Well, that was it. I just hooked up the black and white wires only and left the red unconnected. Attached and it's working. I'm not going to bother at the moment with tracking down the source of the 20 volts on the red wire. I'm sure there is some other old smoke alarm burried in an attic or somewhere else that isn't compatible with my kiddie smoke alarm and that's the red wire issue. For now they are working as standalone alarms and I'm good with that. Thanks to all for your help!
 
  #11  
Old 05-03-16, 03:29 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,983
Received 35 Votes on 30 Posts
The alarms are of limited use if one does not alert to a fire in another part of the building.

The 20 volts may just be phantom voltage.
 
  #12  
Old 05-04-16, 06:39 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,236
Received 39 Votes on 31 Posts
I know that the two that I'm trying to replace are on the same circuit but not sure if there are other alarms or lights or anything else on the circuit or not.
If the detectors are or were interconnected, they'd all have to be on the same circuit.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: