Whar Size Ground Wire Do I Need?

Reply

  #1  
Old 05-02-16, 06:58 PM
S
Member
Thread Starter
Join Date: Jan 2006
Posts: 6
Received 0 Votes on 0 Posts
Whar Size Ground Wire Do I Need?

I an trying to install two 100 watt pole lights at the end of my driveway and a receptacle in a weatherproof box to run a occasional leaf blower or drill. The run from the panel is 465 feet. I have calculated I need #6 wire to make the run with a 5% voltage drop. Question is, do I also need to run a #6 ground as well, or can the ground wire be a small size such as a #8 or #10?
 
  #2  
Old 05-02-16, 07:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,919
Received 1,344 Votes on 1,242 Posts
Wow... that's quite a run.

If you ran the circuit as 240v you would have lower drop on smaller wire but would be forced to use a transformer to convert to 120v.

Are you going to be running the circuit in conduit ?
What size breaker will be feeding the circuit ?
The ground wire can be smaller than the hot and neutral. I believe a #12 green would be adequate.
 
  #3  
Old 05-02-16, 07:05 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,763
Received 97 Votes on 87 Posts
With the #6s, I'd run a #10 ground.
 
  #4  
Old 05-02-16, 07:06 PM
M
Member
Join Date: Sep 2009
Location: Louisville KY
Posts: 577
Received 0 Votes on 0 Posts
The ground wire could certainly be a #8 or a #10 but the question comes down to what kind of cable (wire) are you going to run for the circuit? If you are going to use conduit and pull individual conductors it's very easy to have a different size ground but if you're using direct burial cable you are pretty much at the mercy of the manufacturers as to what combinations they have available.
 

Last edited by Msradell; 05-02-16 at 07:27 PM.
  #5  
Old 05-02-16, 07:11 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,919
Received 1,344 Votes on 1,242 Posts
I based my reply on breaker size. The ground wire would not need to be larger than the supply breaker.
 
  #6  
Old 05-02-16, 08:18 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,513
Received 125 Votes on 99 Posts
Running #6 conductors you have to run a minimum of a #10 ground.
 
  #7  
Old 05-02-16, 08:26 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,224
Received 105 Votes on 91 Posts
The ground would need to be up sized by the same percentage as the hots over the normal size.
 
  #8  
Old 05-04-16, 05:04 AM
S
Member
Thread Starter
Join Date: Jan 2006
Posts: 6
Received 0 Votes on 0 Posts
Yes, I will be pulling THHN through 1" PVC conduit.
 
  #9  
Old 05-04-16, 09:45 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,582
Received 13 Votes on 11 Posts
I will be pulling THHN
You will need THWN not THHN. Most wire is dual rated THHN/THWN just check the labeling on the wire to be sure.
 
 