It's been awhile since a did one of these and want to make sure I have the correct wire sizes.
Connecting a GE subpanel direct lug to a siemens panel. The subpanel is a 125 amp panel direct lug.
I am installing a 100 amp DP breaker in the main and running four 2 guage thhn standard wire to the subpanel. 2 hots, neutral and ground. I removed the bonding screw in the panel.
I planed on running the wires through grey plastic elbow conduit. The main panel is in a corner and mounting the sub on the other corner fits perfectly with the conduit. Is it OK to use the plastic conduit? I have pressure treated 2x4s with a sheet of osb on the wall to mount the panel.
I am running two 4000 watt fan forced heaters from the subpanel. These I have on separate 30 amp dp breakers and am using 10/2 nmb wire (orange Romex).
Does this sound correct? Is the plastic elbow conduit acceptable? Is the 125 amp panel ok with the 100amp breaker?

Thanks in advance.
 
Sponsored Links
  #2  
Old 05-07-16, 03:49 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 55,190
Received 594 Votes on 559 Posts
Since you are running a ground wire.... PVC is ok to use.
10-2 is good for the heater wiring.
By gray plastic elbow do you mean an LB ?

Name:  Z11N9yfo5oy.JPG
Views: 174
Size:  17.7 KB
 
  #3  
Old 05-07-16, 03:55 PM
C
Member
Join Date: May 2015
Location: USA
Posts: 3,138
Received 1 Vote on 1 Post
All sounds good to me. PVC conduit is fine. No problems using a 100 amp breaker to feed 125 amp panel. Breaker and wire size appropriate for the heaters. Use an LB, LL or LR as appropriate if the conduit has to change direction.
 
  #4  
Old 05-07-16, 04:01 PM
H
Member
Thread Starter
Join Date: Oct 2010
Location: USA
Posts: 266
Received 0 Votes on 0 Posts
No just a 90 degree elbow....a solid straight curved piece like this:
Carlon 2 in. 90? Sch. 40 PVC Elbow UA9AJB-CAR at The Home Depot - Mobile

with the flanged end cut off and a glued threaded connector on each end through the knockout on the main and sub
and locked to the panels with nut on the inside. The elbow fits perfectly around the corner from ome to the other.
 
  #5  
Old 05-07-16, 04:09 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 55,190
Received 594 Votes on 559 Posts
Just buy a regular 2" PVC sweep. It won't have the bell end on it.

Name:  sweep.jpg
Views: 186
Size:  2.3 KB
 
  #6  
Old 05-07-16, 07:06 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,279
Received 37 Votes on 31 Posts
Is the #2 copper? The ground can #8 if copper.
 
  #7  
Old 05-12-16, 05:25 AM
H
Member
Thread Starter
Join Date: Oct 2010
Location: USA
Posts: 266
Received 0 Votes on 0 Posts
If I decide to mount the panel on the other side and attach the sub to the main with a straight shot of EMT, I can then skip running the ground wire..correct? ( I Would then just run the two hots and nuetral.)

I would still need to have a separate bus for the neutral and ground in the sub panel and also make sure the bonding screw is removed from the neutral.

Thanks again for the verification.
 
  #8  
Old 05-12-16, 07:58 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 55,190
Received 594 Votes on 559 Posts
I would still run the ground wire.... even with metal conduit.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: