Wiring a 4 gang box, 4 light switches, Power at fixture.

I have a metal gang box with 4 separate light switches- (#1) kitchen; (#2, #3,#4) carport. Incoming cables: switch #1--two 12/3; switch 2, 3, 4.--12/2 to each switch. Switches are on the same circuit. The kitchen light was previously controlled by 3-way. Now disconnected and (1) 12/3 incoming cable taped in gang box.

Incoming Wires
Switch #1 incoming black wire connected to top left screw, incoming white wire to bottom right screw. Red wire to wire nut . Switches 2,3,4 Incoming white wires to wire nut. Switches 2,3,4 Incoming black wires connected to its switch bottom screw. (#1, 2) grounds unattached (#3,4) grounds to switch ground screw.

In box connections
A short white wire connection between Switch #1 bottom screw and switch #2 top screw. A short white wire between switch # 2 top screw to a second wire nut. Short wire from switch #3 and #4 to second wire nut. The result is 2 wires under 1 screw at switch 1 and 2. Presumably these connections are for power distribution to the individual switches.

Does NEC permit 2 wires under one screw? If not, what is the alternative?

Thanks
Ann
 
Sponsored Links
  #2  
Old 05-12-16, 03:26 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
Hi, Ann. Welcome to the best DIY forum on the Internet!

Does NEC permit 2 wires under one screw?
Generally not. The exception is where the screw itself tightens against a pressure plat and the two (straight) conductors enter from the back of the device. This is known as a "back-wired" device and not to be confused with a "back-stabbed" device where the wires are inserted into holes on the back of the switch or receptacle and held in place via spring pressure. The back-stabbed is often thought to be an inferior method of connection and is a common failure point.

The other exception would be if a length of wire had a small center section stripped of insulation and this stripped section was held under the screw head. Of course in this example it isn't really two wires, just a single continuous wire with multiple points of connection.

Back-wired devices are a superior product and are often referred to as "commercial" or "specification" grade and they have a higher price than standard grade devices. They are well worth the additional cost in my opinion.

The alternative is to use what are called "pigtails" where a short piece of wire runs from each device to a "wire nut" where they all join together. Pigtails are very common although the additional junction does make for a potential failure point. In certain instances the use of pigtails is mandated by code such as multi-wire branch circuits (MWBC).

A short white wire connection between Switch #1 bottom screw and switch #2 top screw. A short white wire between switch # 2 top screw to a second wire nut.
The use of white insulated wires in these connections is incorrect. There are few cases when the use of a white wire with a switch is correct and jumping power from switch to switch is not one of them. In most cases a white wire on any switch that does not also contain an indicator light or timing circuit the white is a "hot" (from the controlled fixture) and needs to be re-identified with a color other than white, grey or green.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: