Posts: 266
Received 0 Votes on 0 Posts
subpanel question

I have the neutral and the ground separated in the sub panel. When I run these lines into the main panel does it matter where I connect both the neutral and the ground in the Main panel since the two bus bars are bonded?

Also the subpanel is mounted about eye level on a sheet of mdf next to the main panel. Is it ok to run the new wiring for the branch circuits that go into the subpanel down this mdf? Or would it be better to run conduit to the ceiling as the top of main panel top is much closed to the ceiling?

Thanks
 
Sponsored Links
  #2  
Old 05-17-16, 08:59 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
In the main panel, the neutral should connect to the same bar as the incoming service neutral or to a bar that is firmly bonded to that one. It should not connect to a bar that only connects to the metal box if your main panel is designed that way.

It is standard procedure to staple the incoming romex above the panel to some type of board. Conduit is not necessary in this spot.
 
  #3  
Old 05-17-16, 09:23 AM
Member
Thread Starter
Join Date: Oct 2010
Location: USA
Posts: 266
Received 0 Votes on 0 Posts
Ok.. i got it.. run the neutral to the bus that is directly connected to the bare service neutral that comes in from the street.

Then connect the ground to the bus that is on the opposite side of the panel.
 
  #4  
Old 05-17-16, 09:23 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
The ground can go on either if you have open space. It's just the neutral that should be on the "neutral" bar.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: