Generator wire size for 50 amp backfeed breaker with interlock

I have an intelock kit and I just need verification on the breaker size to use as the backfeed breaker as well as the wire size.

My current generator is 30 amps but I plan on installing a 50 amp inlet box and wiring for 50 amp to the main panel in case i upgrade down the road. Is a 50 amp breaker as the backfeed in the main panel fine or does it need to be higher?

Is the 6 guage romex fine for the 50 amp ? The run is only a few feet to above the panel.


Thanks
 
  #2  
Old 05-18-16, 09:22 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,514
Received 125 Votes on 99 Posts
#6 is correct for 50A. Be sure to use a proper generator power inlet for the cord connection from the generator. Do not make up a cord with male plugs on both ends to backfeed a standard 50A outlet.
 
 