Can the neutral wire tied to the ground make 220V two phase?

Can the neutral wire tied to the ground make 220V two phase?

Reply

  #1  
Old 05-29-16, 08:19 AM
J
Member
Thread Starter
Join Date: May 2016
Location: United States
Posts: 3
Received 0 Votes on 0 Posts
Can the neutral wire tied to the ground make 220V two phase?

Hello,

I live in the US, and I want to install a conveyor dyer that requires 220V single phase and 50 amp. I took some classes on electricity 10 years ago, and little did I do with that knowledge. Now, as far as I know, 220V single phase requires 2 hot wires and 1 ground. 220V two phase, on the other hand, need the two hot wires and the neutral one.

I check my circuit panel today, and I noticed that the neutral in tied to the ground; therefore, if I connect the two hot wire and the ground to the circuit panel, does it not make it two phase since the ground and neutral are tied together? I know two phase is no longer in used, but maybe I am wrong.

Any suggestion will be highly appreciated,
 
Sponsored Links
  #2  
Old 05-29-16, 08:59 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,018
Received 42 Votes on 37 Posts
Two phase power is not used in the US. I think what you are trying to describ eis the difference between a 240 volt only and a 120/240 circuit. The 240 is 2 hots and a ground. 120/240 is 2 hots, a neutral and a ground.
 
  #3  
Old 05-29-16, 10:21 AM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 5,451
Received 0 Votes on 0 Posts
A dryer never uses 2 hot wires and a bare ground, or at least not any dryer I have ever seen.

There are two ways to wire a dryer, 3-wire and 4-wire. The 4-wire is now required, the 3-wire is sometimes grandfathered.

The 3-wire uses the insulated neutral, with the neutral bonded to the chassis with a strip from the terminal block.

The 4-wire uses the neutral and the ground. The neutral is connected to the block and the bonding strip is removed. The ground is connected directly to the chassis.
 
  #4  
Old 05-29-16, 01:43 PM
J
Member
Thread Starter
Join Date: May 2016
Location: United States
Posts: 3
Received 0 Votes on 0 Posts
http://bbcind.com/wp-content/uploads...10/AIR2408.pdf

provided is the link of the conveyor dryer I am talking about. In the circuit panel of the conveyor, there are two breakers and a ground screw. Now, in the main circuit panel of the house, the ground and the neutral (green and white wire) are connected in the same bar; will this (green and white wire are connected in the same bar) affect/damage anything in the dryer? or should I create another ground exclusive for the conveyor?
 
  #5  
Old 05-29-16, 03:02 PM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 5,451
Received 0 Votes on 0 Posts
My comments referred to a clothes dryer, please disregard.
 
  #6  
Old 05-29-16, 03:17 PM
L
Member
Join Date: Nov 2015
Posts: 1,321
Received 41 Votes on 38 Posts
In the US, most residential electricity is wired split phase. It still is a single phase. Not 2 phase.
2 phase is no longer used and as far as I know no one uses 2 phase in the world. 2 phase will have 4 conductors (2 for each phase excluding ground) and no neutral.

As you found out already, Neutral and Ground is tied together at the main circuit breaker panel. Neutral is a center tap from the transformer, thus splitting a single phase 240V into 2 120V circuits.
[ATTACH=CONFIG]66692[/ATTACH]


From what I see in the specification, your dryer does not use 120V at all and will not require neutral. Just connect 2 hot wires from 2 pole breaker to the dryer and a ground.

You do not need to run another ground. If fact, it can be dangerous if that ground is not tied at the breaker panel as a ground fault will not trip the breaker in this case.

You will need 50A 2 pole breaker and 6 AWG wire for your dryer and a outlet matching your dryer cord (unless it is hardwired).
 
Attached Images  

Last edited by lambition; 05-29-16 at 03:47 PM.
  #7  
Old 05-29-16, 11:36 PM
J
Member
Thread Starter
Join Date: May 2016
Location: United States
Posts: 3
Received 0 Votes on 0 Posts
Thank you guys so much for the info. It did help a lot. Enjoy the Memorial Day Holiday!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: