Folks,
I'm building a barn here in Maryland and will run 220V 60 amps from the breaker box in the house to the barn. My plan is to run it underground, probably in PVC. It's about a 200 foot run.
Questions:
1) What type of wire/cable should I use?
2) What gauge should it be?
Needless to say we have a building permit and want to satisfy the inspector.
Thanks!
Jack
I'm building a barn here in Maryland and will run 220V 60 amps from the breaker box in the house to the barn. My plan is to run it underground, probably in PVC. It's about a 200 foot run.
Questions:
1) What type of wire/cable should I use?
2) What gauge should it be?
Needless to say we have a building permit and want to satisfy the inspector.
Thanks!
Jack
#3
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,705
Received 273 Upvotes
on
230 Posts
I highly suggest aluminum 2-2-2-4 Mobile Home Feeder (MHF) for your application. This size is good for 60A at 200ft. I also suggest 2" PVC conduit. If you can't purchase it locally, Wire and Cable to Go on the web is a cheap place to get it even with shipping. http://www.wireandcabletogo.com/2-2-...der-Cable.html